Central heating/boiler problem!!, Help!

Thread Tools
 
Search this Thread
 
Old Jul 29, 2009 | 10:19 PM
  #1  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default Central heating/boiler problem!!, Help!

Right, odd one this!

Its a worcester combi-boiler.

The little gauge that tells you the pressure of the rads keeps going up past 4bar (should normally be 1-2bar) so you have to drain about a litre out the rads. This happens over about 3-4 days. Its only been doing it the past week or 2.

The pipe to connect the boiler to the water supply is disconnected all the time so cant be going in there!

Any plumbers on here!!??
Reply
Old Jul 29, 2009 | 10:26 PM
  #2  
escossie's Avatar
escossie
15000
20 Year Member
 
Joined: Oct 2003
Posts: 19
Likes: 0
From: uk
Default

Sounds like its the hot water heat exchanger passing between the mains water & primary water so chances are you need a new heat exchanger. Which worcester combi is it?
Reply
Old Jul 29, 2009 | 10:28 PM
  #3  
TIFF's Avatar
TIFF
Chasing Radders
 
Joined: May 2003
Posts: 37,253
Likes: 2
From: WARWICK
Default

Well if there is no water going into the system............there is 2 outcomes.

1-The gauge is fucked

Or

2-The water is finding its way into the heating system via the hot water side....which i am not 100% sure it can as they are 2 seperate systems.

I would test the gauge first......or even fit a auxillery one on the flow pipe. That way you will see the pressure iin the heating system.

If you dont release the pressure, does it fire the Blow off valve and empty itself???
Reply
Old Jul 29, 2009 | 10:32 PM
  #4  
TIFF's Avatar
TIFF
Chasing Radders
 
Joined: May 2003
Posts: 37,253
Likes: 2
From: WARWICK
Default

Could possible need the expansion vessel re-charging as this can sometimes make the pressure creep up.........

The red expansion vessel has a valve on it that you connect a foot pump/bike pump to. Make sure it is reading 1.5 bar.........if it isnt, pump it up to this pressure. That may fix the issue
Reply
Old Jul 29, 2009 | 10:36 PM
  #5  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Originally Posted by escossie
Sounds like its the hot water heat exchanger passing between the mains water & primary water so chances are you need a new heat exchanger. Which worcester combi is it?
Not 100% sure, quite a big one tho (12 rads i think)

Will get model number tmrw
Reply
Old Jul 29, 2009 | 10:37 PM
  #6  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Originally Posted by TIFF
Could possible need the expansion vessel re-charging as this can sometimes make the pressure creep up.........

The red expansion vessel has a valve on it that you connect a foot pump/bike pump to. Make sure it is reading 1.5 bar.........if it isnt, pump it up to this pressure. That may fix the issue
Thats for help, i've read that 3 times and my tiny mind cant make sense of it lol
Reply
Old Jul 29, 2009 | 10:38 PM
  #7  
ryan81's Avatar
ryan81
Regular Contributor
 
Joined: Nov 2005
Posts: 208
Likes: 0
From: Jersey Ci
Default

is the filling loop disconected or jsut in the isolate posistion ?

if its completely disconnected it`s the heat exchanger, if its in the isolate pos it could be by passing
Reply
Old Jul 29, 2009 | 10:39 PM
  #8  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Originally Posted by ryan11
is the filling loop disconected or jsut in the isolate posistion ?

if its completely disconnected it`s the heat exchanger, if its in the isolate pos it could be by passing
Completly removed mate
Reply
Old Jul 29, 2009 | 10:40 PM
  #9  
TIFF's Avatar
TIFF
Chasing Radders
 
Joined: May 2003
Posts: 37,253
Likes: 2
From: WARWICK
Default

I will try and make it easier for you Neil.......lol

If you turn the boiler off, then remove the front cover.....usually a few screws.........

You will see a red vessel at the back i think it is......this is the expension vessel.

On it will be like a tyre valve that you use to blow the tyre up with. Stick a pump or gauge on it and see what it is reading. It should be 1.5bar........

If it isnt, pump it up to that
Reply
Old Jul 29, 2009 | 10:42 PM
  #10  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Originally Posted by TIFF
I will try and make it easier for you Neil.......lol

If you turn the boiler off, then remove the front cover.....usually a few screws.........

You will see a red vessel at the back i think it is......this is the expension vessel.

On it will be like a tyre valve that you use to blow the tyre up with. Stick a pump or gauge on it and see what it is reading. It should be 1.5bar........

If it isnt, pump it up to that
LOL, thats better mate, remember i'm thick!

I'm not taking the covers off mate, i will almost certainly kill myself!
Reply
Old Jul 29, 2009 | 10:43 PM
  #11  
TIFF's Avatar
TIFF
Chasing Radders
 
Joined: May 2003
Posts: 37,253
Likes: 2
From: WARWICK
Default

Neil.....if you turn the fuse spur off to it you will be fine.........
Reply
Old Jul 29, 2009 | 10:45 PM
  #12  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Originally Posted by TIFF
Neil.....if you turn the fuse spur off to it you will be fine.........
Its on a plug mate so all good

I havnt got owt to check pressure anyway, best ring a plumber tmrw..... more money down the drain!
Reply
Old Jul 29, 2009 | 10:46 PM
  #13  
ryan81's Avatar
ryan81
Regular Contributor
 
Joined: Nov 2005
Posts: 208
Likes: 0
From: Jersey Ci
Default

Originally Posted by Neil Clark
Completly removed mate
well if it`s removed , i would say its your HX (heat exchanger ) at fault , an hours labour + part
Reply
Old Jul 29, 2009 | 11:46 PM
  #14  
Fewkesy's Avatar
Fewkesy
Wahay!! I've lost my Virginity!!
 
Joined: Nov 2005
Posts: 72
Likes: 0
From: Nottingham
Default

AS above mate.
will be your plate heat exchanged pinholed internally. could only be a vessel fault if you have been running your heating but i doubt it at the moment.
this is becoming quite common at the moment due to sludge build up in the system. a good product to add while your changing it is a magnaclean. They are brilliant and will help stop it happenning again.

hope this helps
Reply
Old Jul 30, 2009 | 05:49 AM
  #15  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Originally Posted by Fewkesy
AS above mate.
will be your plate heat exchanged pinholed internally. could only be a vessel fault if you have been running your heating but i doubt it at the moment.
this is becoming quite common at the moment due to sludge build up in the system. a good product to add while your changing it is a magnaclean. They are brilliant and will help stop it happenning again.

hope this helps
Not a plumber are you? i'm only in Derby!
Reply
Old Jul 30, 2009 | 06:15 AM
  #16  
Cragrat's Avatar
Cragrat
sit boo boo sit
15 Year Member
Liked
iTrader: (4)
 
Joined: Jun 2008
Posts: 8,006
Likes: 50
From: Location Location..
Default

try ringing their technical helpline bud 08705266241

its 24hr

always been helpfull to me
Reply
Old Jul 30, 2009 | 08:27 AM
  #17  
RSTurboSI's Avatar
RSTurboSI
BANNED
iTrader: (1)
 
Joined: Aug 2008
Posts: 2,718
Likes: 0
From: Nottinghamshire
Default

give exitpoint a Pm..but best if you call him heres his contact page.

http://www.plumbromany.co.uk/

hes in nottingham, and use me as a referance. Simon colton.

hes a real good mate. so will make sure you are sorted.

Last edited by RSTurboSI; Jul 30, 2009 at 08:28 AM.
Reply
Old Jul 30, 2009 | 09:45 AM
  #18  
TIFF's Avatar
TIFF
Chasing Radders
 
Joined: May 2003
Posts: 37,253
Likes: 2
From: WARWICK
Default

Originally Posted by Fewkesy
a good product to add while your changing it is a magnaclean. They are brilliant and will help stop it happenning again.

hope this helps

I always fit these now.....superb product
Reply
Old Jul 31, 2009 | 12:01 AM
  #19  
Fewkesy's Avatar
Fewkesy
Wahay!! I've lost my Virginity!!
 
Joined: Nov 2005
Posts: 72
Likes: 0
From: Nottingham
Thumbs up

Originally Posted by Neil Clark
Not a plumber are you? i'm only in Derby!
yea i am mate. i work for british gas on the breakdown side.
if you struggle to get some1 then let me know.
Reply
Old Jul 31, 2009 | 06:15 AM
  #20  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Cheers all!

Got worcester coming on Monday, one off payment off Ł210 and will fix any problem (they say!)
Reply
Old Jul 31, 2009 | 04:29 PM
  #21  
Steve the Plumber's Avatar
Steve the Plumber
The original Rouge Trader
iTrader: (11)
 
Joined: Nov 2007
Posts: 4,288
Likes: 3
From: Charing
Default

Have you got very high mains water pressure?
Reply
Old Jul 31, 2009 | 09:56 PM
  #22  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Originally Posted by Steve the Plumber
Have you got very high mains water pressure?
Dont think so, just normal i think
Reply
Old Aug 1, 2009 | 10:35 AM
  #23  
Jon(M600BHP)'s Avatar
Jon(M600BHP)
I've found that life I needed.. It's HERE!!
 
Joined: May 2006
Posts: 1,027
Likes: 0
Default

More than likely the little pipe feeding the expansion vessel is blocked or as said above the vessel has lost its charge, So just needs draining down and expansion vessel pipe removing and cleaning and vessel pressure checking But deffo get an engineer to do it thx Jon
Reply
Old Aug 1, 2009 | 10:56 AM
  #24  
TIFF's Avatar
TIFF
Chasing Radders
 
Joined: May 2003
Posts: 37,253
Likes: 2
From: WARWICK
Default

Funnily enough Neil....i had a call out yesterday for the exact same thing as yours......And like i said in my earlier post, It was the expension vessel needed recharging....

I charged them Ł50..............
Reply
Old Aug 1, 2009 | 03:57 PM
  #25  
Neil Clark's Avatar
Neil Clark
Thread Starter
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,890
Likes: 1
Default

Originally Posted by TIFF
Funnily enough Neil....i had a call out yesterday for the exact same thing as yours......And like i said in my earlier post, It was the expension vessel needed recharging....

I charged them Ł50..............
Come as far as Derby for work mate?
Reply
Old Aug 2, 2009 | 05:37 PM
  #26  
TIFF's Avatar
TIFF
Chasing Radders
 
Joined: May 2003
Posts: 37,253
Likes: 2
From: WARWICK
Default

lol...........if i was closer i would mate.......
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
DAZZER
Ford Escort RS Turbo
5
Sep 30, 2015 08:43 PM
DavidK
Ford Sierra/Sapphire/RS500 Cosworth
1
Sep 27, 2015 02:55 PM
Russ Payne
Ford Sierra/Sapphire/RS500 Cosworth
1
Sep 25, 2015 08:29 PM
morg65
Escort MK 5 / MK 6
3
Sep 23, 2015 08:57 PM




All times are GMT. The time now is 03:32 PM.