Any good plumbers that might be able to help
Any help would be much appreciated.
My small water expansion tank in the loft is full of boiling water.I noticed this the other day as the ballcock imploded. The boiler runs for about ten minutes then the pipes start banging ,the 3 port valve starts clicking, The water pump sounds like glass flowing through it.The boiler trips off and a load of boiling water comes out the open vent pipe into the expansion tank.
You can then hear the boiler trying to start again with the fan clicking on and off for a few minutes. Then it all fires up again.
I don't think its ever worked well. I'v changed the pcb and the water pump.
I'v also drained the system before and there was no black sludge. I wonder could the system need flushing as there may be bad water flow?
My small water expansion tank in the loft is full of boiling water.I noticed this the other day as the ballcock imploded. The boiler runs for about ten minutes then the pipes start banging ,the 3 port valve starts clicking, The water pump sounds like glass flowing through it.The boiler trips off and a load of boiling water comes out the open vent pipe into the expansion tank.
You can then hear the boiler trying to start again with the fan clicking on and off for a few minutes. Then it all fires up again.
I don't think its ever worked well. I'v changed the pcb and the water pump.
I'v also drained the system before and there was no black sludge. I wonder could the system need flushing as there may be bad water flow?
#2
10K+ Poster!!
If it runs for tens mins with no probs then starts to make the noises it sounds like the thermostat on the boiler is faulty and its boiling the system.
There should be an over heat cut off on the boiler but that sounds like thats faulty too.
I take it your a a corgi reg gas engineer yeah?
There should be an over heat cut off on the boiler but that sounds like thats faulty too.
I take it your a a corgi reg gas engineer yeah?
#5
E36 cosworth
Thread Starter
Join Date: Dec 2005
Location: bedfordshire
Posts: 547
Likes: 0
Received 0 Likes
on
0 Posts
I'm looking at the wiring diagram
and found
Lo thermostat
Hi thermostat
overheat run off device
pump ???errun thermostat (cannot read what it says)
I'll get my friend from British gas to buy and fit the parts as he has diagnosed it wrong and already cost me.Thanks for the help.
I'v actually started a plumbing course at college this summer.
I have asked my lecturer and she told me that the water pump is in the wrong place and the pipe work needs reconfiguring.
As she just said this of the top of her head and the house was only built in 1994 I very much doubt this is the case.
and found
Lo thermostat
Hi thermostat
overheat run off device
pump ???errun thermostat (cannot read what it says)
I'll get my friend from British gas to buy and fit the parts as he has diagnosed it wrong and already cost me.Thanks for the help.
I'v actually started a plumbing course at college this summer.
I have asked my lecturer and she told me that the water pump is in the wrong place and the pipe work needs reconfiguring.
As she just said this of the top of her head and the house was only built in 1994 I very much doubt this is the case.
Trending Topics
#9
E36 cosworth
Thread Starter
Join Date: Dec 2005
Location: bedfordshire
Posts: 547
Likes: 0
Received 0 Likes
on
0 Posts
The overflow is not dripping. I found out the tank had boiling water in it as the week before the ballcock had imploded and I had been keeping an eye on it, and I have changed it. Just looked at the boiler and there are 2 water pipes on the top. One has a drain valve, Should I drain the system from here,Then connect a hose pipe here and flush it through? I'm in Luton.
#10
The original Rouge Trader
iTrader: (11)
If its a blocked system then normal draining and flushing wont do, IF its a blocked system a good power flush may cure your problem, failing that get somebody out you can trust not to rip you off and have a look for you, but chances are you've got a blockage somewhere in the airing cupboard.
Diagonosing is'nt always easy over the web, but we're all try to help!
Diagonosing is'nt always easy over the web, but we're all try to help!
#12
PassionFord Post Whore!!
Keeps the pump running after the burner has switched off, to cool the heat exchanger down.
Has it always banged or is it recent?
Is the boiler, Wall mounted, floor mounted, upstairs or downstairs.?
What make and is it the original boiler? (does the pipework near the boiler look like it's been altered to fit a new boiler)
.
.
Last edited by focusv8; 04-01-2009 at 09:56 AM.
#13
E36 cosworth
Thread Starter
Join Date: Dec 2005
Location: bedfordshire
Posts: 547
Likes: 0
Received 0 Likes
on
0 Posts
My boiler is a myson apollo 50 and is feeding 6 small radiators.
The boiler has never seemed to be right as cuts in and out too often. The banging and boiling water going to the expansion tank has only just started to happen.
My boiler is wallmounted and my house is a 2 bedroomed coach house (all rooms are one level) house was built in 1994 and I'm pretty sure its the original boiler.
Today I changed the Lo stat,Hi stat and limit stat.
The Boiling water has stopped going in the expansion tank and no more banging,But the boiler now runs 30 seconds on 30 seconds off. It is heating the radiators and water but I know this is not right.
Is this right I'v brought a bottle of fernox heavy duty restorer and Im going to put it in my system for 7 days and then flush the system and see what happens.
I'v been told the myson appollo has a very small heat exchanger and might be blocked with lime scale.
The boiler has never seemed to be right as cuts in and out too often. The banging and boiling water going to the expansion tank has only just started to happen.
My boiler is wallmounted and my house is a 2 bedroomed coach house (all rooms are one level) house was built in 1994 and I'm pretty sure its the original boiler.
Today I changed the Lo stat,Hi stat and limit stat.
The Boiling water has stopped going in the expansion tank and no more banging,But the boiler now runs 30 seconds on 30 seconds off. It is heating the radiators and water but I know this is not right.
Is this right I'v brought a bottle of fernox heavy duty restorer and Im going to put it in my system for 7 days and then flush the system and see what happens.
I'v been told the myson appollo has a very small heat exchanger and might be blocked with lime scale.
#14
PassionFord Post Troll
iTrader: (8)
I had this exact same problem last year, I found that the thermostat probe that sits in the boiler had split so was not switching the boiler off once the water was up to temp, so the water was getting to hot after 10 mins or so and sending it up the expansion pipe and into the top up tank for the rads. Bought one for a couple of quid and fitted it and not had any problems since
#15
E36 cosworth
Thread Starter
Join Date: Dec 2005
Location: bedfordshire
Posts: 547
Likes: 0
Received 0 Likes
on
0 Posts
I changed the Lo stat,Hi stat and limit stat today and the water is not boiling up any more,but it is working fine now no boiling water or noises but the boiler runs 30 seconds on 30 seconds off.
#16
Baby Cheesus
iTrader: (4)
i have had problems with mine too, you may have seen my thread.
anyway, it was cutting in and out very often, i now think due to a partially seized pump. i say partially as it would then run and pump water ok after a while
i have ust replaced the pump and so far, all seems to be ok
you say you have already changed the pump tho..
anyway, it was cutting in and out very often, i now think due to a partially seized pump. i say partially as it would then run and pump water ok after a while
i have ust replaced the pump and so far, all seems to be ok
you say you have already changed the pump tho..
#17
E36 cosworth
Thread Starter
Join Date: Dec 2005
Location: bedfordshire
Posts: 547
Likes: 0
Received 0 Likes
on
0 Posts
I changed the pump about 7 months ago. This was the first thing I did ,the arrow is pointing towards the 3 port valve.
I wonder if the water has been boiling over if the new pump may be damaged ?
You can feel the pump running and when you change the speeds feel the pump slow down or speed up.
I wonder if the water has been boiling over if the new pump may be damaged ?
You can feel the pump running and when you change the speeds feel the pump slow down or speed up.
#18
The original Rouge Trader
iTrader: (11)
I changed the pump about 7 months ago. This was the first thing I did ,the arrow is pointing towards the 3 port valve.
I wonder if the water has been boiling over if the new pump may be damaged ?
You can feel the pump running and when you change the speeds feel the pump slow down or speed up.
I wonder if the water has been boiling over if the new pump may be damaged ?
You can feel the pump running and when you change the speeds feel the pump slow down or speed up.
Hot water wont damage the pump, they are designed to get hot,
Sorry mate, my monies on the cold feed!
#19
E36 cosworth
Thread Starter
Join Date: Dec 2005
Location: bedfordshire
Posts: 547
Likes: 0
Received 0 Likes
on
0 Posts
At the weekend im going to drain the system. Try and blow some of the pipes through with nitrogen and put heavy duty restorer in the system for 7 days as the bottle says.
As said a few posts above. The thermostat must have been broken aswell as the water is not going into the expansion tank anymore.
Steve the plumber . I take it you mean the cold water feed to the boiler. All the help is much apreciated. thanks
As said a few posts above. The thermostat must have been broken aswell as the water is not going into the expansion tank anymore.
Steve the plumber . I take it you mean the cold water feed to the boiler. All the help is much apreciated. thanks
Last edited by e30cossie; 08-01-2009 at 06:56 PM.
#20
The original Rouge Trader
iTrader: (11)
At the weekend im going to drain the system. Try and blow some of the pipes through with nitrogen and put heavy duty restorer in the system for 7 days as the bottle says.
As said a few posts above. The thermostat must have been broken aswell as the water is not going into the expansion tank anymore.
Steve the plumber . I take it you mean the cold water feed to the boiler. All the help is much apreciated. thanks
As said a few posts above. The thermostat must have been broken aswell as the water is not going into the expansion tank anymore.
Steve the plumber . I take it you mean the cold water feed to the boiler. All the help is much apreciated. thanks
Its the cold feed pipe from the little tank in the loft to the airing cupboard, normaly goes to a air separater (looks like a swirl pot) and has the pump normaly attached to the same pipe, that the cold feed and it normaly clogs up from the from the pipe that comes bottom of the air sep down to the pump region, but i do say NORMALY, because yours could be designed differently and it could be blocked elsewhere.
#22
On the subject of boilers.
Firstly I know FECK ALL about them so prepare for some really noob terms
I have a typical boiler and hot water tank system in a new house (built 4 years ago).
The boiler is in the utility room and whenever I go on holiday for a week or two (I live it heating the house, but obviously I don't use any of the hot water for the taps etc) I come back and the pressure has dropped and the boiler has turned itself off.
The only visible issue is a thin brown sticky residue sitting below the boiler. I have tried time and time to locate where the liquid is coming from and it "looks" like it is coming from the solid black (size of a decent apple) thing that MIGHT be the pump (as said, total noob).
It also now drops the pressure quite frequently - I would guess every week or two max, even with regular use.
Anyone got any ideas? Do I just need to get a pro out to have a look at the pump? It all operates fine but that leak is annoying
Cheers
RW
Firstly I know FECK ALL about them so prepare for some really noob terms
I have a typical boiler and hot water tank system in a new house (built 4 years ago).
The boiler is in the utility room and whenever I go on holiday for a week or two (I live it heating the house, but obviously I don't use any of the hot water for the taps etc) I come back and the pressure has dropped and the boiler has turned itself off.
The only visible issue is a thin brown sticky residue sitting below the boiler. I have tried time and time to locate where the liquid is coming from and it "looks" like it is coming from the solid black (size of a decent apple) thing that MIGHT be the pump (as said, total noob).
It also now drops the pressure quite frequently - I would guess every week or two max, even with regular use.
Anyone got any ideas? Do I just need to get a pro out to have a look at the pump? It all operates fine but that leak is annoying
Cheers
RW
#23
The original Rouge Trader
iTrader: (11)
On the subject of boilers.
Firstly I know FECK ALL about them so prepare for some really noob terms
I have a typical boiler and hot water tank system in a new house (built 4 years ago).
The boiler is in the utility room and whenever I go on holiday for a week or two (I live it heating the house, but obviously I don't use any of the hot water for the taps etc) I come back and the pressure has dropped and the boiler has turned itself off.
The only visible issue is a thin brown sticky residue sitting below the boiler. I have tried time and time to locate where the liquid is coming from and it "looks" like it is coming from the solid black (size of a decent apple) thing that MIGHT be the pump (as said, total noob).
It also now drops the pressure quite frequently - I would guess every week or two max, even with regular use.
Anyone got any ideas? Do I just need to get a pro out to have a look at the pump? It all operates fine but that leak is annoying
Cheers
RW
Firstly I know FECK ALL about them so prepare for some really noob terms
I have a typical boiler and hot water tank system in a new house (built 4 years ago).
The boiler is in the utility room and whenever I go on holiday for a week or two (I live it heating the house, but obviously I don't use any of the hot water for the taps etc) I come back and the pressure has dropped and the boiler has turned itself off.
The only visible issue is a thin brown sticky residue sitting below the boiler. I have tried time and time to locate where the liquid is coming from and it "looks" like it is coming from the solid black (size of a decent apple) thing that MIGHT be the pump (as said, total noob).
It also now drops the pressure quite frequently - I would guess every week or two max, even with regular use.
Anyone got any ideas? Do I just need to get a pro out to have a look at the pump? It all operates fine but that leak is annoying
Cheers
RW
If it is, it could be leaking out of the pressure relief valve outside, or even the auto air vent could be weaping?
#24
Thanks
RW
#25
Too many posts.. I need a life!!
Join Date: Nov 2004
Location: In the Sticks!!
Posts: 986
Likes: 0
Received 0 Likes
on
0 Posts
At the weekend im going to drain the system. Try and blow some of the pipes through with nitrogen and put heavy duty restorer in the system for 7 days as the bottle says.
As said a few posts above. The thermostat must have been broken aswell as the water is not going into the expansion tank anymore.
Steve the plumber . I take it you mean the cold water feed to the boiler. All the help is much apreciated. thanks
As said a few posts above. The thermostat must have been broken aswell as the water is not going into the expansion tank anymore.
Steve the plumber . I take it you mean the cold water feed to the boiler. All the help is much apreciated. thanks
#26
Too many posts.. I need a life!!
Join Date: Nov 2004
Location: In the Sticks!!
Posts: 986
Likes: 0
Received 0 Likes
on
0 Posts
On the subject of boilers.
Firstly I know FECK ALL about them so prepare for some really noob terms
I have a typical boiler and hot water tank system in a new house (built 4 years ago).
The boiler is in the utility room and whenever I go on holiday for a week or two (I live it heating the house, but obviously I don't use any of the hot water for the taps etc) I come back and the pressure has dropped and the boiler has turned itself off.
The only visible issue is a thin brown sticky residue sitting below the boiler. I have tried time and time to locate where the liquid is coming from and it "looks" like it is coming from the solid black (size of a decent apple) thing that MIGHT be the pump (as said, total noob).
It also now drops the pressure quite frequently - I would guess every week or two max, even with regular use.
Anyone got any ideas? Do I just need to get a pro out to have a look at the pump? It all operates fine but that leak is annoying
Cheers
RW
Firstly I know FECK ALL about them so prepare for some really noob terms
I have a typical boiler and hot water tank system in a new house (built 4 years ago).
The boiler is in the utility room and whenever I go on holiday for a week or two (I live it heating the house, but obviously I don't use any of the hot water for the taps etc) I come back and the pressure has dropped and the boiler has turned itself off.
The only visible issue is a thin brown sticky residue sitting below the boiler. I have tried time and time to locate where the liquid is coming from and it "looks" like it is coming from the solid black (size of a decent apple) thing that MIGHT be the pump (as said, total noob).
It also now drops the pressure quite frequently - I would guess every week or two max, even with regular use.
Anyone got any ideas? Do I just need to get a pro out to have a look at the pump? It all operates fine but that leak is annoying