Evening all.

Wondered if some one could help. I appreciate this is notifiable works and will not be connected up or tested by us however the cable run and logistics and buying of the bits will be done DIY.

Parents have a Static Caravan they have bought back from the coast due to my Dad being long term poorly. They want to use it for storage and perhaps sitting out their in the summer. The would like to run a feed of power to it and would like it done properly. There is a consumer board in the house and the caravan.

I have a shopping list in my head, however would like to know what a sparky would need to do, so I know my folks are not going to get ripped off.

The van has a 16amp male commando socket end on it!

-Armoured Cable with an ambiant (Not buried run of around 30 Metres) What conductive area will each core need to be?
- How many cores will it need to be?
- WIll it need its own earth rod?
- On the house consumer board what size fuse would be needed.

Again just to state the connecting and testing WILL NOT be done by us. Purely the run and hole drilling etc.

Cheers
Lee
Old 10-10-2010, 07:12 PM
  #2  
St3V3_C
PassionFord Post Whore!!
 
St3V3_C's Avatar
 
Join Date: May 2003
Location: Bristol
Posts: 9,580
Received 42 Likes on 36 Posts
Default

2.5mm2
3 core is best so you don't rely on armour earth.
No earth rod
16A

There is already an RCD there somewhere right?
Old 10-10-2010, 07:16 PM
  #3  
S3an
PassionFord Post Troll
 
S3an's Avatar
 
Join Date: Jan 2005
Location: Workington Cumbria
Posts: 3,377
Received 14 Likes on 13 Posts
Default

will only need 3 core cable. would only get 2.5mm. you could run it off a 30amp breaker if you wanted as you will probably need its own consumer inside the van aswell.
Old 10-10-2010, 07:18 PM
  #4  
L33 BYT
PassionFord Post Whore!!

Thread Starter
 
L33 BYT's Avatar
 
Join Date: Jul 2003
Location: SUFFOLK
Posts: 7,482
Likes: 0
Received 0 Likes on 0 Posts
Default

I'll get some more details however from the quick look I had at the House consumer, there is one main RCD before it goes into the fuse box, which I understand isnt really ideal as if something pop's it takes the lot out. Not sure if this is a problem but there is only a yellow (20 Amp) slot spare so not sure if the Consumer in the house needs a swap out.
The caravan end is slightly newer and think the 2 rings for sockets are on the RCD side.

If its using the house Earth is that suitable?

Cheers
Lee
Old 10-10-2010, 07:18 PM
  #5  
S3an
PassionFord Post Troll
 
S3an's Avatar
 
Join Date: Jan 2005
Location: Workington Cumbria
Posts: 3,377
Received 14 Likes on 13 Posts
Default

you sound pretty competent to me, why not try it yourself. can only try if you get stuck theres always PF to keep you right.
Old 10-10-2010, 07:20 PM
  #6  
St3V3_C
PassionFord Post Whore!!
 
St3V3_C's Avatar
 
Join Date: May 2003
Location: Bristol
Posts: 9,580
Received 42 Likes on 36 Posts
Default

Originally Posted by S3an
will only need 3 core cable. would only get 2.5mm. you could run it off a 30amp breaker
If you do use 32A ( you mean 32 not 30 right ) then cable will need to be 6mm.

you will probably need its own consumer inside the van aswell.
?
He is just installing a 16A socket.
Old 10-10-2010, 07:21 PM
  #7  
L33 BYT
PassionFord Post Whore!!

Thread Starter
 
L33 BYT's Avatar
 
Join Date: Jul 2003
Location: SUFFOLK
Posts: 7,482
Likes: 0
Received 0 Likes on 0 Posts
Default

Im a telecoms engineer by trade, so often come up against power. However I am actually scared of electric and popped on a DIY forum and got shot down saying it must be done by part P person and documented.
Old 10-10-2010, 07:21 PM
  #8  
cozzy940
Too many posts.. I need a life!!
 
cozzy940's Avatar
 
Join Date: Sep 2006
Location: norfolk
Posts: 789
Likes: 0
Received 0 Likes on 0 Posts
Default

Originally Posted by St3V3_C
2.5mm2
3 core is best so you don't rely on armour earth.
No earth rod
16A

There is already an RCD there somewhere right?
earth rod will be needed you shouldnt use earth from house supply as main earth, caravan should be seperately staked
Old 10-10-2010, 07:26 PM
  #9  
St3V3_C
PassionFord Post Whore!!
 
St3V3_C's Avatar
 
Join Date: May 2003
Location: Bristol
Posts: 9,580
Received 42 Likes on 36 Posts
Default

So the house board is old re-wireable fuse type?

You can go from that, but a new board really is money well spent dude.

House earth is fine as its an outside socket. If you were installing a separate board it would need a rod, as far as I know.

However, if the house stuff is all pretty old, your whole earthing situation will probably want looking at...
Old 10-10-2010, 07:34 PM
  #10  
L33 BYT
PassionFord Post Whore!!

Thread Starter
 
L33 BYT's Avatar
 
Join Date: Jul 2003
Location: SUFFOLK
Posts: 7,482
Likes: 0
Received 0 Likes on 0 Posts
Default

Steve, not sure if fuses are re-wireable, they are the MCB type B (I think by comparason on Screwfix) if that has any meaning to this whole conversation. Also would need to rod in that case as in the van there is a seperate consumer unit, its just been tailed to a 16amp commando which then used to uplink into the carvan park power when it was sited.

So, ideally thinking logically let me think basic.
Say the carvan was designed to trip 20amp, then really it would be better if the house fuse was larger eg 30 amp, this way if the van tripped it wouldnt trip the house. (Hoping my thinking is right here)

30 Amp, will need a 6mm Core - Check,
Earth Stake - Check,

If having its own Earth rod then, does the 3rd core come into account?

Last edited by L33 BYT; 10-10-2010 at 07:42 PM.
Old 10-10-2010, 07:42 PM
  #11  
St3V3_C
PassionFord Post Whore!!
 
St3V3_C's Avatar
 
Join Date: May 2003
Location: Bristol
Posts: 9,580
Received 42 Likes on 36 Posts
Default

EDIT: I'm not sure enough, so check with the guy fitting it all up though, and let us know what he says!

Last edited by St3V3_C; 10-10-2010 at 07:50 PM.
Old 10-10-2010, 09:32 PM
  #12  
vaughant
PassionFord Post Whore!!
iTrader: (1)
 
vaughant's Avatar
 
Join Date: Jun 2008
Location: south wales, swansea
Posts: 6,807
Received 0 Likes on 0 Posts
Default

Hi fella,the earthing rod is a great system (TT system) but be careful if the ground where the caravans going to be sited is sandy as you may struggle to get a good enough earth,it makes it difficult for the sparky to get good readings to pass it off then and after all it is for their protection.

The readings can be improved by making the ground moist where the rod is inserted but often screwing one rod into another to get down deeper is fine.

6mm cable sounds good to me,2.5 would have been a bit thin IMHO,there's nit a huge price difference either.

There's a lot of shit spouted on forums but people are pretty good on here,I did a caravan live last year by wearing a thick rubber glove to connect it to the mains,I'm still here,common sense really.

The yellow fuse/mcb was traditionally used for immersion heaters which most houses don't really use now hence their usually spare,my garage runs off it in my old house!!!
Old 10-10-2010, 09:37 PM
  #13  
vaughant
PassionFord Post Whore!!
iTrader: (1)
 
vaughant's Avatar
 
Join Date: Jun 2008
Location: south wales, swansea
Posts: 6,807
Received 0 Likes on 0 Posts
Default

Btw,try tlc for electrical stuff as well,their gland kits for armoured are brilliant,everything you'll need and not that expensive either.use a copper pipe cutter to get through the armoured sheathing and metal underneath,only cost you about Ł5,whereas their specialist ones cost about Ł20 and don't really do the job any better.

Also,if you use 3 core as suggested above,remember to get the correct earth and neutral sheathing as the three core colours are brown,black and grey so you'll need to sheath the black and grey in blue and green/yellow to comply with regs.

Last edited by vaughant; 10-10-2010 at 09:42 PM.
Old 10-10-2010, 09:52 PM
  #14  
cjwood555
Advanced PassionFord User
 
cjwood555's Avatar
 
Join Date: Feb 2005
Location: Solihull
Posts: 2,090
Likes: 0
Received 0 Likes on 0 Posts
Default

To avoid Part P notification, and on the basis that you're just laying the cable on the ground anyway, make up an extension lead from a 13A RCD plug to 16A ceeform. 2.5mm^2 will suffice @ 30m / 16A.

Job jobbed.
Old 11-10-2010, 09:01 PM
  #15  
art411y
Too many posts.. I need a life!!
iTrader: (1)
 
art411y's Avatar
 
Join Date: Oct 2004
Location: grimsby
Posts: 536
Likes: 0
Received 0 Likes on 0 Posts
Default

without seeing the job i would use a 60 or 100amp henly block from your existing incoming supply.t would be a good time to upgrade your board tails to 25mm and 16mm earth unless already had upgrade.i would not use the home board and ibstall a small garage board with a 60amp main switch and a 40 amp rcbo to the caravan or a 40amp cb if the caravan board has its own rcd.6mm supply would be ample for small to medium sized caravans.had varied results with earthing rods so would prefer to run a seperate 10mm earth along side the 16mm armoured.if glanding off is a problem in either board then a 4mm x4mm ip44 or above plastic or galv box would make life easier
Old 11-10-2010, 09:37 PM
  #16  
dojj
Resident Wrestling Legend
iTrader: (3)
 
dojj's Avatar
 
Join Date: May 2003
Location: Little India
Posts: 50,018
Received 258 Likes on 221 Posts
Default

by adding the caravan to the main fuseboard, will it take it over the rated max?

if the electrics are old anyway, it might be worth getting the whole house done, or at least the consumer unit changed to one that will handle the upgrades

the earhting thing will be taken care of by the guy who wires it up so best to take their recomendations on it as we don't know if the ground is earthable where the caravan is going to be, assuming it'd be hard standing as a static caravan and not letf on 2 wheels and a pole like the top gear stuff?
Old 11-10-2010, 10:04 PM
  #17  
fraser9764
PassionFord Post Troll
iTrader: (3)
 
fraser9764's Avatar
 
Join Date: Oct 2006
Location: Cheshire
Posts: 3,070
Received 29 Likes on 23 Posts
Default

crikey theres some people on here who like to make a big job of things! you're not pricing for the job, no need to add unnecesary extras to bump up the price a bit!
all you are doing is adding a 16a socket, nothing big or fancy.
i would run the cable in 2.5mm SWA for protection and stick a 16a plug on the end, put a 16a waterproof socket on the side of the house and run the supply back in 2.5mm twin and earth to a new breaker on the consumer unit. job jobbed.
just make sure you aren't overloading the consumer unit and its rcd protected.

Last edited by fraser9764; 11-10-2010 at 10:06 PM.
Old 11-10-2010, 10:33 PM
  #18  
xr4x4rs
10K+ Poster!!
iTrader: (5)
 
xr4x4rs's Avatar
 
Join Date: May 2004
Location: coventry
Posts: 10,574
Likes: 0
Received 3 Likes on 3 Posts
Default

shame your so far away as i bought a 100m reel of armoured core cable for my garage and used about 20m
Old 12-10-2010, 07:30 PM
  #19  
L33 BYT
PassionFord Post Whore!!

Thread Starter
 
L33 BYT's Avatar
 
Join Date: Jul 2003
Location: SUFFOLK
Posts: 7,482
Likes: 0
Received 0 Likes on 0 Posts
Default

cheers for the replies guys. Ill sort some better details of what the house has already.

Lee
Old 12-10-2010, 09:11 PM
  #20  
GARETH T
Professional Waffler
 
GARETH T's Avatar
 
Join Date: May 2003
Location: barry-south wales
Posts: 30,980
Received 9 Likes on 6 Posts
Default

Originally Posted by fraser9764
crikey theres some people on here who like to make a big job of things! you're not pricing for the job, no need to add unnecesary extras to bump up the price a bit!
all you are doing is adding a 16a socket, nothing big or fancy.
i would run the cable in 2.5mm SWA for protection and stick a 16a plug on the end, put a 16a waterproof socket on the side of the house and run the supply back in 2.5mm twin and earth to a new breaker on the consumer unit. job jobbed.
just make sure you aren't overloading the consumer unit and its rcd protected.

this is the way i would do it!
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
jc1989rs
General Car Related Discussion.
3
18-09-2015 07:05 PM
sparkys2turbo
Restorations, Rebuilds & Projects.
16
05-01-2012 03:29 PM
sparkys2turbo
Pictures, video & Photoshop Forum
6
29-07-2011 12:41 PM
sparkys2turbo
Cars for Sale
18
16-05-2010 12:17 AM
sparkys2turbo
General Car Related Discussion.
9
09-05-2010 10:00 PM



Quick Reply: Sparky Help Please :-) What do I need to do..............



All times are GMT. The time now is 03:09 AM.