Default any electricians about!!

Hi my next door neighbour is after advice about her heater for her outdoor pool.
Its a 5kilowatt unit , whats the best/safest way to power it? will it be fine just plugged into mains or should she have it rigged into the mains via its own fuse board etc....
forgive me if this is a daft question , wot i know on electrics i could write on a pin head.
any replys much appreciated ,mike
Old 24-05-2009, 01:12 PM
  #2  
markyrst
Wahay!! I've lost my Virginity!!
 
markyrst's Avatar
 
Join Date: Oct 2005
Location: lisburn n. ireland
Posts: 75
Received 0 Likes on 0 Posts
Default

5kw will be pullin about 22 amps so if its pluged into a 13 amp socket it will blow immediatley. its gona need probably a 32 amp 4mm supply on a 30mA rcd
Old 24-05-2009, 01:13 PM
  #3  
opposite lock
PassionFord Post Troll
Thread Starter
iTrader: (3)
 
opposite lock's Avatar
 
Join Date: May 2005
Location: essex,
Posts: 2,504
Received 3 Likes on 3 Posts
Thumbs up

Originally Posted by markyrst
5kw will be pullin about 22 amps so if its pluged into a 13 amp socket it will blow immediatley. its gona need probably a 32 amp 4mm supply on a 30mA rcd
thanks pal thts great
Old 24-05-2009, 01:19 PM
  #4  
dreamer
PassionFord Regular
 
dreamer's Avatar
 
Join Date: Apr 2006
Location: Nsw
Posts: 417
Likes: 0
Received 0 Likes on 0 Posts
Default

Will that be goin constantly?

Might justify a 3 phase connection in the long run depending on what way it works out

Contact a pool specialist deffo
Old 24-05-2009, 01:22 PM
  #5  
markyrst
Wahay!! I've lost my Virginity!!
 
markyrst's Avatar
 
Join Date: Oct 2005
Location: lisburn n. ireland
Posts: 75
Received 0 Likes on 0 Posts
Default

3 phase will cost a fortune to get put in, couldnt be justified in a domestic situation
Old 24-05-2009, 02:10 PM
  #6  
KSA-Cossie
Professional Waffler
iTrader: (4)
 
KSA-Cossie's Avatar
 
Join Date: May 2004
Location: Shutting down jap crap
Posts: 25,439
Received 19 Likes on 17 Posts
Default

Originally Posted by markyrst
5kw will be pullin about 22 amps so if its pluged into a 13 amp socket it will blow immediatley. its gona need probably a 32 amp 4mm supply on a 30mA rcd
As above depending on cable run.
Old 24-05-2009, 02:13 PM
  #7  
daveselwood
Too many posts.. I need a life!!
 
daveselwood's Avatar
 
Join Date: Aug 2006
Location: conwy
Posts: 541
Likes: 0
Received 0 Likes on 0 Posts
Default

you need to work out the volt drop for the cable distance,how many amps does it run,how many meters away from fuse box and it will definatly need an rcd,,in,the 17edition wiring regs there is a section devoted to swimming pools,post up the amps and distance in meters and ill work it out for you
Old 24-05-2009, 02:49 PM
  #8  
Shandy-Ade
Advanced PassionFord User
 
Shandy-Ade's Avatar
 
Join Date: Jul 2004
Location: West London
Posts: 2,394
Likes: 0
Received 0 Likes on 0 Posts
Default

I had this problem when i wanted a 9kw heater, tell her to buy a 3kw heater then it can be plugged into a normal plug depending how far the cable run is
Old 24-05-2009, 04:10 PM
  #9  
opposite lock
PassionFord Post Troll
Thread Starter
iTrader: (3)
 
opposite lock's Avatar
 
Join Date: May 2005
Location: essex,
Posts: 2,504
Received 3 Likes on 3 Posts
Default

Originally Posted by daveselwood
you need to work out the volt drop for the cable distance,how many amps does it run,how many meters away from fuse box and it will definatly need an rcd,,in,the 17edition wiring regs there is a section devoted to swimming pools,post up the amps and distance in meters and ill work it out for you
ok m8 thanks i,ll speak to neighbour right away ,
Old 24-05-2009, 04:31 PM
  #10  
opposite lock
PassionFord Post Troll
Thread Starter
iTrader: (3)
 
opposite lock's Avatar
 
Join Date: May 2005
Location: essex,
Posts: 2,504
Received 3 Likes on 3 Posts
Default

Originally Posted by daveselwood
you need to work out the volt drop for the cable distance,how many amps does it run,how many meters away from fuse box and it will definatly need an rcd,,in,the 17edition wiring regs there is a section devoted to swimming pools,post up the amps and distance in meters and ill work it out for you
hi, 20m from house fuse box
rated voltage 220-240
rated power 5000 watts
frequeny 50 hz
cant see how many amps it runs !!!
Old 24-05-2009, 05:56 PM
  #11  
daveselwood
Too many posts.. I need a life!!
 
daveselwood's Avatar
 
Join Date: Aug 2006
Location: conwy
Posts: 541
Likes: 0
Received 0 Likes on 0 Posts
Default

5000 divide 230=22amps,you can get away with 2.5mm,but id use 4 mm with a 30 milliamp rcd protecting it and a 25amp mcb.if in doubt get an approved sparky in to do the job as swimming pools are like bathrooms and have zones that you have to use certain types of ip rated equipment in
Old 24-05-2009, 06:31 PM
  #12  
danneth
TORQUE!
 
danneth's Avatar
 
Join Date: Sep 2006
Location: Sheffield
Posts: 11,756
Received 3 Likes on 3 Posts
Default

Originally Posted by daveselwood
5000 divide 230=22amps,you can get away with 2.5mm,but id use 4 mm with a 30 milliamp rcd protecting it and a 25amp mcb.if in doubt get an approved sparky in to do the job as swimming pools are like bathrooms and have zones that you have to use certain types of ip rated equipment in

which make boards do you use ive never seen a 25a mcb personally ???
Old 24-05-2009, 06:47 PM
  #13  
daveselwood
Too many posts.. I need a life!!
 
daveselwood's Avatar
 
Join Date: Aug 2006
Location: conwy
Posts: 541
Likes: 0
Received 0 Likes on 0 Posts
Default

Originally Posted by danneth
which make boards do you use ive never seen a 25a mcb personally ???
meant 25amp rcd
Old 24-05-2009, 08:19 PM
  #14  
cozzy940
Too many posts.. I need a life!!
 
cozzy940's Avatar
 
Join Date: Sep 2006
Location: norfolk
Posts: 789
Likes: 0
Received 0 Likes on 0 Posts
Default

i wouldnt put 4mm on 32 a supply , 6mm supply on 32a will be fine
Old 24-05-2009, 08:22 PM
  #15  
opposite lock
PassionFord Post Troll
Thread Starter
iTrader: (3)
 
opposite lock's Avatar
 
Join Date: May 2005
Location: essex,
Posts: 2,504
Received 3 Likes on 3 Posts
Thumbs up

Originally Posted by daveselwood
5000 divide 230=22amps,you can get away with 2.5mm,but id use 4 mm with a 30 milliamp rcd protecting it and a 25amp mcb.if in doubt get an approved sparky in to do the job as swimming pools are like bathrooms and have zones that you have to use certain types of ip rated equipment in
thanks for tht i,ll let her know , just for the record roughly how much should this roughly be costing to install proffesionaly? sounds like a nice setup tho!!!!
Old 24-05-2009, 08:24 PM
  #16  
Cragrat
sit boo boo sit
iTrader: (4)
 
Cragrat's Avatar
 
Join Date: Jun 2008
Location: Location Location..
Posts: 8,006
Received 50 Likes on 44 Posts
Default

Originally Posted by daveselwood
5000 divide 230=22amps,you can get away with 2.5mm,but id use 4 mm with a 30 milliamp rcd protecting it and a 25amp mcb.if in doubt get an approved sparky in to do the job as swimming pools are like bathrooms and have zones that you have to use certain types of ip rated equipment in

job will have to be done by a part p registered sparky as not only is it a notifiable job its government legislation it be done by one

end of
Old 24-05-2009, 08:32 PM
  #17  
rstdave
PassionFord Post Troll
iTrader: (3)
 
rstdave's Avatar
 
Join Date: Jan 2005
Location: Bristol/Bath
Posts: 2,568
Likes: 0
Received 0 Likes on 0 Posts
Default

6mm swa fed via 32a mcb/30ma rcd feeding a 32a rotary switch should do the job, ideally double poled isolation back at the fuse board end.
Old 24-05-2009, 08:33 PM
  #18  
opposite lock
PassionFord Post Troll
Thread Starter
iTrader: (3)
 
opposite lock's Avatar
 
Join Date: May 2005
Location: essex,
Posts: 2,504
Received 3 Likes on 3 Posts
Default

thanks everyone for ur views and info on this , i,ll pass it all on and leave it their hands.!!!! its one for the pro,s so its nice she,s now got a got idea it whats involved.

job done

any ideas on cost of this setup ? roughly . sounds like quite few hours job to me

Last edited by opposite lock; 24-05-2009 at 08:37 PM. Reason: update
Old 24-05-2009, 08:44 PM
  #19  
focusv8
PassionFord Post Whore!!
 
focusv8's Avatar
 
Join Date: Sep 2004
Location: Nottingham
Posts: 4,772
Received 86 Likes on 81 Posts
Default

Originally Posted by danneth
which make boards do you use ive never seen a 25a mcb personally ???
You don't get out much then;

http://www.voltimum.co.uk/catalog/pr...lin-Gerin.html

.
Old 24-05-2009, 08:53 PM
  #20  
rstdave
PassionFord Post Troll
iTrader: (3)
 
rstdave's Avatar
 
Join Date: Jan 2005
Location: Bristol/Bath
Posts: 2,568
Likes: 0
Received 0 Likes on 0 Posts
Default

25a mcb's aren't commonplace to use/be seen in a domestic fuse board though are they, think that's what the guy was getting at.
Old 24-05-2009, 09:01 PM
  #21  
opposite lock
PassionFord Post Troll
Thread Starter
iTrader: (3)
 
opposite lock's Avatar
 
Join Date: May 2005
Location: essex,
Posts: 2,504
Received 3 Likes on 3 Posts
Red face

Originally Posted by rstdave
25a mcb's aren't commonplace to use/be seen in a domestic fuse board though are they, think that's what the guy was getting at.
i did say to her surely it should run seperately . we just measured the length the wiring will be from her fuse board in garage.
So exactly at what point to you live the system? forgive me but i dont have a clue lol sorry guys!
Old 24-05-2009, 09:02 PM
  #22  
Cragrat
sit boo boo sit
iTrader: (4)
 
Cragrat's Avatar
 
Join Date: Jun 2008
Location: Location Location..
Posts: 8,006
Received 50 Likes on 44 Posts
Default

Originally Posted by opposite lock
thanks everyone for ur views and info on this , i,ll pass it all on and leave it their hands.!!!! its one for the pro,s so its nice she,s now got a got idea it whats involved.

job done

any ideas on cost of this setup ? roughly . sounds like quite few hours job to me

to do right yes it wont be cheap but unfortunately there are lot of lads about will do it cheap-but you know what you will get in the long run if they go down that route

really annoys me at the moment that the layman knows nowt about part-p but all about what was corgi (but thats another argument)

without seeing i wouldnt imagine they`ll get much change from Ł500-Ł600

that is site unseen tho
Old 24-05-2009, 09:07 PM
  #23  
danneth
TORQUE!
 
danneth's Avatar
 
Join Date: Sep 2006
Location: Sheffield
Posts: 11,756
Received 3 Likes on 3 Posts
Default

Originally Posted by focusv8

i get out quite often thanks, just never seen one hence the question
Old 24-05-2009, 09:16 PM
  #24  
opposite lock
PassionFord Post Troll
Thread Starter
iTrader: (3)
 
opposite lock's Avatar
 
Join Date: May 2005
Location: essex,
Posts: 2,504
Received 3 Likes on 3 Posts
Default

Originally Posted by Cragrat
to do right yes it wont be cheap but unfortunately there are lot of lads about will do it cheap-but you know what you will get in the long run if they go down that route

really annoys me at the moment that the layman knows nowt about part-p but all about what was corgi (but thats another argument)

without seeing i wouldnt imagine they`ll get much change from Ł500-Ł600

that is site unseen tho
yep i agree abt the corgi thing. You would think there would a 'corgi' for you sparkies hence next door tryin to heat god knows how many gallons of water. Its 18ft by 10 or 12 ft ,4ft deep. how many litres/gallons there lol. perhaps thts for a different thread lol but once again thanks
Old 24-05-2009, 09:36 PM
  #25  
rstdave
PassionFord Post Troll
iTrader: (3)
 
rstdave's Avatar
 
Join Date: Jan 2005
Location: Bristol/Bath
Posts: 2,568
Likes: 0
Received 0 Likes on 0 Posts
Default

Originally Posted by opposite lock
i did say to her surely it should run seperately . we just measured the length the wiring will be from her fuse board in garage.
So exactly at what point to you live the system? forgive me but i dont have a clue lol sorry guys!
Run directly from the fuse board on its own circuit yes. Would be live coming out the fuseboard then i would suggest putting an isolator at the swimming pool (a switch to turn it off) for ease of use.
Old 24-05-2009, 10:03 PM
  #26  
opposite lock
PassionFord Post Troll
Thread Starter
iTrader: (3)
 
opposite lock's Avatar
 
Join Date: May 2005
Location: essex,
Posts: 2,504
Received 3 Likes on 3 Posts
Thumbs up

i see.....yes the switch is a good idea
Old 24-05-2009, 11:04 PM
  #27  
daveselwood
Too many posts.. I need a life!!
 
daveselwood's Avatar
 
Join Date: Aug 2006
Location: conwy
Posts: 541
Likes: 0
Received 0 Likes on 0 Posts
Default

Originally Posted by cozzy940
i wouldnt put 4mm on 32 a supply , 6mm supply on 32a will be fine
why 4mm takes 37 amps when buried
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
van_dogg_pavvy
Technical help Q & A
2
03-03-2016 09:30 AM
BillyCabrio
General Car Related Discussion.
21
07-03-2008 12:22 AM
geoffxr4
General Car Related Discussion.
6
02-11-2006 09:00 AM
DaveEscos
General Car Related Discussion.
4
11-02-2005 11:33 AM



Quick Reply: any electricians about!!



All times are GMT. The time now is 11:33 PM.