PF Plumbers
I know that there are some plumbers on here, I was just wondering if you could help?
It is a problem i am having with the Boiler , Baxi 105(combi)
When i am running hot water for a bath after about 30 seconds the water starts to run cold for about 20 seconds then warms up again , its as though the boiler keeps cutting off and letting the water go cold .
It seems ok when you are having a shower and the central heating works (i did notice theat the little LED above the flame symbal took a while to come on when i first started the central heating)
thanks for any help
It is a problem i am having with the Boiler , Baxi 105(combi)
When i am running hot water for a bath after about 30 seconds the water starts to run cold for about 20 seconds then warms up again , its as though the boiler keeps cutting off and letting the water go cold .
It seems ok when you are having a shower and the central heating works (i did notice theat the little LED above the flame symbal took a while to come on when i first started the central heating)
thanks for any help
I know that there are some plumbers on here, I was just wondering if you could help?
It is a problem i am having with the Boiler , Baxi 105(combi)
When i am running hot water for a bath after about 30 seconds the water starts to run cold for about 20 seconds then warms up again , its as though the boiler keeps cutting off and letting the water go cold .
It seems ok when you are having a shower and the central heating works (i did notice theat the little LED above the flame symbal took a while to come on when i first started the central heating)
thanks for any help
It is a problem i am having with the Boiler , Baxi 105(combi)
When i am running hot water for a bath after about 30 seconds the water starts to run cold for about 20 seconds then warms up again , its as though the boiler keeps cutting off and letting the water go cold .
It seems ok when you are having a shower and the central heating works (i did notice theat the little LED above the flame symbal took a while to come on when i first started the central heating)
thanks for any help

Just had this on mine
was the divertor valve sticking causing the thermistor on the c/h pipe to cut the boiler out.
To test it leave your heating off until it cools down, identify the c/h pipe out from the boiler, then put your hot water on , if the c/h pipe gets hot then the divertor is sticking. Easy to get from most plumber supplies places PTS, Wickes etc and really easy to change, just did mine and what a difference
Must admit I did clean out the heat plate as well but it was definetly the divertor sticking for my problem.
To test it leave your heating off until it cools down, identify the c/h pipe out from the boiler, then put your hot water on , if the c/h pipe gets hot then the divertor is sticking. Easy to get from most plumber supplies places PTS, Wickes etc and really easy to change, just did mine and what a difference
Must admit I did clean out the heat plate as well but it was definetly the divertor sticking for my problem.
Last edited by snoopaloopa; Jan 15, 2009 at 08:32 PM.
You would be better off just replacing the thermistor(s) first, they are cheaper and easier to DIY and then you can see if its cured it or not with out a lot of outlay.
Thread
Thread Starter
Forum
Replies
Last Post
Christian and Beccy
General Car Related Discussion.
13
May 6, 2006 09:50 PM
Fiecos Dan
General Car Related Discussion.
3
May 1, 2006 08:25 PM