Central heating experts help needed

Thread Tools
 
Search this Thread
 
Old Dec 5, 2007 | 06:24 PM
  #1  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default Central heating experts help needed

Three of the radiators in my house are stone cold the others are roasting,i've tried to bleed them but no air comes out only water.
If i bleed off about a pint of water the radiator starts to heat up at the bottom but once i stop bleeding the water it goes cold again,any tips please ??
Reply
Old Dec 5, 2007 | 07:07 PM
  #2  
Escos Jam's Avatar
Escos Jam
I've found that life I needed.. It's HERE!!
 
Joined: Mar 2005
Posts: 1,235
Likes: 5
From: Central Scotland
Default

Get Euan on the case mate. He'l sort ya out
Reply
Old Dec 5, 2007 | 07:11 PM
  #3  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Mr Begbie are you there.
Reply
Old Dec 5, 2007 | 07:12 PM
  #4  
nilrem's Avatar
nilrem
STOP!... Carry on
 
Joined: Dec 2006
Posts: 2,200
Likes: 0
From: Derbyshire
Default

are you bleeding the highest radiator? apart form that im unsure...
Reply
Old Dec 5, 2007 | 07:18 PM
  #5  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

All on one level m8
Reply
Old Dec 5, 2007 | 07:21 PM
  #6  
turbo_3dr_tommy's Avatar
turbo_3dr_tommy
Advanced PassionFord User
 
Joined: Nov 2005
Posts: 1,693
Likes: 0
From: Newton Aycliffe
Default

turn the radiators off which are heating up that should push the heat to the cold rads, also sounds like the system needs balancing
Reply
Old Dec 5, 2007 | 07:27 PM
  #7  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Whats balancing m8 ?
Reply

Trending Topics

Old Dec 5, 2007 | 07:34 PM
  #8  
turbo_3dr_tommy's Avatar
turbo_3dr_tommy
Advanced PassionFord User
 
Joined: Nov 2005
Posts: 1,693
Likes: 0
From: Newton Aycliffe
Default

balancing means to balance the flow to each radiator.

what you need to do is take the cover off the loack shield valve (the oposite valve to the one you can turn) and screw in the valve on each of the radiators which heat up quickly.
Reply
Old Dec 5, 2007 | 07:35 PM
  #9  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Cheers for that m8.
Reply
Old Dec 5, 2007 | 07:40 PM
  #10  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

has this just happend Kev?
Reply
Old Dec 5, 2007 | 07:42 PM
  #11  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

More or less over the last week euan
Reply
Old Dec 5, 2007 | 07:48 PM
  #12  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

What kind of boiler is it mate...
Reply
Old Dec 5, 2007 | 07:52 PM
  #13  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Combi , how do i get the plastic head off the thermostat valve at the rad ??
Reply
Old Dec 5, 2007 | 07:53 PM
  #14  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

Dont rush in mate....

Read me the exact model and make from the fron of the boiler
Reply
Old Dec 5, 2007 | 08:00 PM
  #15  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Ideal mini c28 m8.
Reply
Old Dec 5, 2007 | 08:02 PM
  #16  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

Whats the presure at?
Reply
Old Dec 5, 2007 | 08:04 PM
  #17  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

1.5 bar
Reply
Old Dec 5, 2007 | 08:09 PM
  #18  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

everything seems cool then.

turn all the rads off athen turn on each of the problem ones and make sure they heat up
Reply
Old Dec 5, 2007 | 08:12 PM
  #19  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Doing that now m8,is it a blockage somewhere ? Weird that when i drained off water the bottom of the rad heated up .
Reply
Old Dec 5, 2007 | 08:14 PM
  #20  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

seems as their is a restriction somewhere mate...

what colour is the water coming out the rads?
Reply
Old Dec 5, 2007 | 08:15 PM
  #21  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

The one in the bog was black the others were clear.
Reply
Old Dec 5, 2007 | 08:18 PM
  #22  
Steve the Plumber's Avatar
Steve the Plumber
The original Rouge Trader
iTrader: (11)
 
Joined: Nov 2007
Posts: 4,288
Likes: 3
From: Charing
Default

Have the non heating up rads have thermostatic rad valves (trv) fitted?, if yes then try to unscrew the trv head only, and push the little pin which is now exposed on the trv body in and out GENTLY, wait a couple of seconds and the pipe leading to the rads may start to heat up. The trv may be stuck and might need some gentle encouragement with a hammer to the the body of the trv to free it!

If not, the system may need balancing?
Reply
Old Dec 5, 2007 | 08:18 PM
  #23  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

black water usually means blockages or the start of problems.


this can be cured by adding chemicals to the system but its not really a job for a DIY'er no disrespect mate.

Best thing to do in short term is let the boiler pump to each of the prob rads only(all others closed) for ten mins to try and clear any partial blockages then open all the rads and report back
Reply
Old Dec 5, 2007 | 08:21 PM
  #24  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Originally Posted by Steve the Plumber
Have the non heating up rads have thermostatic rad valves (trv) fitted?, if yes then try to unscrew the trv head only and push the little pin which is now exposed on the trv body in and out GENTLY, wait a couple of seconds and the pipe leading to the rads may start to heat up.

If not balance the system may need balancing?
How does the plastic head come off ?
Reply
Old Dec 5, 2007 | 08:21 PM
  #25  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Originally Posted by rapidcossie
black water usually means blockages or the start of problems.


this can be cured by adding chemicals to the system but its not really a job for a DIY'er no disrespect mate.

Best thing to do in short term is let the boiler pump to each of the prob rads only(all others closed) for ten mins to try and clear any partial blockages then open all the rads and report back
Will do euan thats a beer im owe ya m8.
Reply
Old Dec 5, 2007 | 08:22 PM
  #26  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

Unlikely that 3 TRVS have jammed at the exact same time...

We need to know what kind of rad valves before I can say how to take them off.

Take a pic?

Systems dont tend to just need balenced after years of working perfectly unless there is somekind of restriction forming..
Reply
Old Dec 5, 2007 | 08:26 PM
  #27  
Steve the Plumber's Avatar
Steve the Plumber
The original Rouge Trader
iTrader: (11)
 
Joined: Nov 2007
Posts: 4,288
Likes: 3
From: Charing
Default

If the water is that black and sludgie out of the system, just adding a chemical into the system is a waste of time and effort, you'd be better off getting someone in to power flush the boiler and system!
Reply
Old Dec 5, 2007 | 08:27 PM
  #28  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Valves are westherm if that helps at all.
Reply
Old Dec 5, 2007 | 08:29 PM
  #29  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

Originally Posted by Steve the Plumber
If the water is that black and sludgie out of the system, just adding a chemical into the system is a waste of time and effort, you'd be better off getting someone in to power flush the boiler and system!

tell him the price and wait for him to faint
Reply
Old Dec 5, 2007 | 08:30 PM
  #30  
Steve the Plumber's Avatar
Steve the Plumber
The original Rouge Trader
iTrader: (11)
 
Joined: Nov 2007
Posts: 4,288
Likes: 3
From: Charing
Default

Originally Posted by KSA-Cossie
Originally Posted by Steve the Plumber
Have the non heating up rads have thermostatic rad valves (trv) fitted?, if yes then try to unscrew the trv head only and push the little pin which is now exposed on the trv body in and out GENTLY, wait a couple of seconds and the pipe leading to the rads may start to heat up.

If not balance the system may need balancing?
How does the plastic head come off ?
Just below the plastic trv head is normaly a chrome lock nut type thing, use some adjustable grips to undo.
Reply
Old Dec 5, 2007 | 08:30 PM
  #31  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

I heard its hundreds .
Reply
Old Dec 5, 2007 | 08:32 PM
  #32  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

Scot gas charge 600 ish mate

Dont worry too much just now tho...

Any of your mates plumbers asit easier to get them in to try the basics frist
Reply
Old Dec 5, 2007 | 08:32 PM
  #33  
Steve the Plumber's Avatar
Steve the Plumber
The original Rouge Trader
iTrader: (11)
 
Joined: Nov 2007
Posts: 4,288
Likes: 3
From: Charing
Default

Originally Posted by rapidcossie
Originally Posted by Steve the Plumber
If the water is that black and sludgie out of the system, just adding a chemical into the system is a waste of time and effort, you'd be better off getting someone in to power flush the boiler and system!

tell him the price and wait for him to faint

Anything between £250-£500, Ker-ching
Reply
Old Dec 5, 2007 | 08:44 PM
  #34  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Originally Posted by rapidcossie
Unlikely that 3 TRVS have jammed at the exact same time...
Unlikely but they were all stuck but now freed off what could i use to lube them ?

Thanks very much to you and steve euan.
Reply
Old Dec 5, 2007 | 08:51 PM
  #35  
Steve the Plumber's Avatar
Steve the Plumber
The original Rouge Trader
iTrader: (11)
 
Joined: Nov 2007
Posts: 4,288
Likes: 3
From: Charing
Default

Well done, you should be warm and toasty now!

Theres no need to lube them because they stick internally, turn them up and down now again, or give them a good whack if they stick again! LOL
Reply
Old Dec 5, 2007 | 08:55 PM
  #36  
KSA-Cossie's Avatar
KSA-Cossie
Thread Starter
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Will do m8 thanks again.
Reply
Old Dec 5, 2007 | 09:26 PM
  #37  
rapidcossie's Avatar
rapidcossie
10K+ Poster!!
 
Joined: May 2004
Posts: 14,907
Likes: 1
From: scotland
Default

I was wrong

you could just take the heads off for a while then the valves acant shut and jam
Reply
Old Dec 5, 2007 | 11:16 PM
  #38  
rigwrecker's Avatar
rigwrecker
Advanced PassionFord User
 
Joined: Jul 2005
Posts: 1,709
Likes: 0
From: thurso far far north of scotland
Default

if ur brave u can pull the pin outwith a pair off pliers put some grease on the pin and push it back in but have an old sheet and some kitchen roll ready once back in move out and in a few times to free up the valve
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
JPA
Ford RS Turbo Parts for Sale
3
Nov 8, 2015 12:26 PM
Johnsie
Ford Focus ST
4
Sep 8, 2015 02:39 PM
Seanyfarrell
Technical help Q & A
0
Aug 14, 2015 11:37 PM
track.focus'd
Restorations, Rebuilds & Projects.
26
Aug 12, 2015 05:53 PM
col93saphcos
Ford Sierra/Sapphire/RS500 Cosworth
5
Aug 7, 2015 03:21 PM




All times are GMT. The time now is 07:52 AM.