FAO PLUMBER boiler problems
right i have a saunier duval boiler ISOFAST F28 E and it constantly lets water out of the drain pipe!! i have changed the heating safety valve and the problem still occurs!
the wierd thing is the bolier system never seems to need re-filling
does any of the experts on here have an idea to what it could be?
Cheers,
Hardeep
the wierd thing is the bolier system never seems to need re-filling
does any of the experts on here have an idea to what it could be?
Cheers,
Hardeep
#2
I've found that life I needed.. It's HERE!!
Join Date: May 2004
Location: middlesex
Posts: 1,206
Likes: 0
Received 0 Likes
on
0 Posts
check that the filling loop is completly closed, sounds like its sluightly open so filling up with too much pressure and opening pressure relief valve