I've just bought a 10.9kw Mira shower, whats the thickness cable i need?

Is it ok to put a short piece of wire on it with a plug and plug it into the extension lead?

Old 22-06-2005, 07:08 PM
  #2  
BillyCabrio
10K+ Poster!!
Thread Starter
iTrader: (1)
 
BillyCabrio's Avatar
 
Join Date: Jun 2003
Location: Dartford, Kent - Home of the two way one way system.
Posts: 13,450
Received 2 Likes on 2 Posts
Default

Not really I do know better than that!

Just wanna double check its the same cable as Electric cooker applications?

Along with the double pole switch and RCD in the fuse box

Cheers lol
Old 22-06-2005, 07:11 PM
  #3  
Graceland
Team HOTHOT!

 
Graceland's Avatar
 
Join Date: Aug 2003
Location: Huddersfield Drives: Trains ;)
Posts: 19,065
Received 1 Like on 1 Post
Default

4mm twin and earth, on its own circuit breaker in the consumer unit - need to have a 16ms trip time so the breaker is a catagory B one i think - was years ago when i did all this at college
Old 22-06-2005, 07:21 PM
  #4  
BillyCabrio
10K+ Poster!!
Thread Starter
iTrader: (1)
 
BillyCabrio's Avatar
 
Join Date: Jun 2003
Location: Dartford, Kent - Home of the two way one way system.
Posts: 13,450
Received 2 Likes on 2 Posts
Default

Yeah i knew about the breaker, so 4mm then. Cheers.
Old 22-06-2005, 07:22 PM
  #5  
focusv8
PassionFord Post Whore!!
 
focusv8's Avatar
 
Join Date: Sep 2004
Location: Nottingham
Posts: 4,770
Received 86 Likes on 81 Posts
Default

It needs to be AT LEAST 10mm twin and earth, depends how long the cable is going to be. (earth loop impedance) or you better get an insurance claim form ready.

Disclaimer:

Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
Old 22-06-2005, 07:24 PM
  #6  
Graceland
Team HOTHOT!

 
Graceland's Avatar
 
Join Date: Aug 2003
Location: Huddersfield Drives: Trains ;)
Posts: 19,065
Received 1 Like on 1 Post
Default

10mm twin and earth - thats way to heavy - we never used to even fit anything above 4mm armoured for 12kw machinery when i was a maintenance bod
Old 22-06-2005, 07:28 PM
  #7  
GARETH T
Professional Waffler
 
GARETH T's Avatar
 
Join Date: May 2003
Location: barry-south wales
Posts: 30,980
Received 9 Likes on 6 Posts
Default

i havent got my cablee tables at home with me (anyone got the 16th edition iee?) but im sure you on the edge of 10mm, but it should be fine

of cause it all depends on the cable run

Trending Topics

Old 22-06-2005, 07:29 PM
  #8  
GARETH T
Professional Waffler
 
GARETH T's Avatar
 
Join Date: May 2003
Location: barry-south wales
Posts: 30,980
Received 9 Likes on 6 Posts
Default

Originally Posted by Graceland
10mm twin and earth - thats way to heavy - we never used to even fit anything above 4mm armoured for 12kw machinery when i was a maintenance bod
whats that 3phase machinery though?
Old 22-06-2005, 07:29 PM
  #9  
focusv8
PassionFord Post Whore!!
 
focusv8's Avatar
 
Join Date: Sep 2004
Location: Nottingham
Posts: 4,770
Received 86 Likes on 81 Posts
Default

That'll be 12kw 3 Phase....think about it..
Old 22-06-2005, 07:30 PM
  #10  
Graceland
Team HOTHOT!

 
Graceland's Avatar
 
Join Date: Aug 2003
Location: Huddersfield Drives: Trains ;)
Posts: 19,065
Received 1 Like on 1 Post
Default

thats a good point - 3 different phases to distrbute the current - my excuse is i aint put any of the theory into practice in about 4 years
Old 22-06-2005, 07:32 PM
  #11  
Graceland
Team HOTHOT!

 
Graceland's Avatar
 
Join Date: Aug 2003
Location: Huddersfield Drives: Trains ;)
Posts: 19,065
Received 1 Like on 1 Post
Default

voltage drop, ambient temperature, resistence of the cable and heat generation are more of a factor in single phase from what i remember - its ages since i studdied it, might have to dig my 16th edition regs book out
Old 22-06-2005, 07:35 PM
  #12  
GARETH T
Professional Waffler
 
GARETH T's Avatar
 
Join Date: May 2003
Location: barry-south wales
Posts: 30,980
Received 9 Likes on 6 Posts
Default

might have to dig my 16th edition regs book out

ya its an exciting coarse isnt it
Old 22-06-2005, 07:36 PM
  #13  
Graceland
Team HOTHOT!

 
Graceland's Avatar
 
Join Date: Aug 2003
Location: Huddersfield Drives: Trains ;)
Posts: 19,065
Received 1 Like on 1 Post
Default

never did the 16th edition course - i walked out of my job, they were going to put me thru it tho - kinda wish i stayed now and got 16th edition qualified - altho i left with onc and hnc in electrical engineering - but i've forgotten nearly all of it
Old 22-06-2005, 07:44 PM
  #14  
Graceland
Team HOTHOT!

 
Graceland's Avatar
 
Join Date: Aug 2003
Location: Huddersfield Drives: Trains ;)
Posts: 19,065
Received 1 Like on 1 Post
Default

http://www.tlc-direct.co.uk/Book/4.3.9.htm

data and cable tables
Old 22-06-2005, 07:54 PM
  #15  
BillyCabrio
10K+ Poster!!
Thread Starter
iTrader: (1)
 
BillyCabrio's Avatar
 
Join Date: Jun 2003
Location: Dartford, Kent - Home of the two way one way system.
Posts: 13,450
Received 2 Likes on 2 Posts
Default

Originally Posted by focusv8
Disclaimer:

Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
I'm aware of the new regs, all i wanna do is the cable run to save on labour cost. I'll get a sparkie to connect it either end.

I'll ask a sparkie at work tomorrow.
Old 22-06-2005, 07:58 PM
  #16  
KSA-Cossie
Professional Waffler
iTrader: (4)
 
KSA-Cossie's Avatar
 
Join Date: May 2004
Location: Shutting down jap crap
Posts: 25,439
Received 19 Likes on 17 Posts
Default

10 mm twin and earth m8.
Old 22-06-2005, 08:01 PM
  #17  
GARETH T
Professional Waffler
 
GARETH T's Avatar
 
Join Date: May 2003
Location: barry-south wales
Posts: 30,980
Received 9 Likes on 6 Posts
Default

focusv8,
Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.

the mad thing is,, my boss is charman of the south wales IEE, he bought a house for his girl, the morgage company wanted a certificate to say the electrics of the house was up too spec,,,,, he wasnt alowed to write one as he wasnt approved
Old 22-06-2005, 08:07 PM
  #18  
Graceland
Team HOTHOT!

 
Graceland's Avatar
 
Join Date: Aug 2003
Location: Huddersfield Drives: Trains ;)
Posts: 19,065
Received 1 Like on 1 Post
Default

thats a bit shit really
Old 22-06-2005, 08:08 PM
  #19  
BillyCabrio
10K+ Poster!!
Thread Starter
iTrader: (1)
 
BillyCabrio's Avatar
 
Join Date: Jun 2003
Location: Dartford, Kent - Home of the two way one way system.
Posts: 13,450
Received 2 Likes on 2 Posts
Default

I'm 99.9% sure its a 45amp rated cable tho
Old 22-06-2005, 08:10 PM
  #20  
GARETH T
Professional Waffler
 
GARETH T's Avatar
 
Join Date: May 2003
Location: barry-south wales
Posts: 30,980
Received 9 Likes on 6 Posts
Default

Originally Posted by BillyCabrio
I'm 99.9% sure its a 45amp rated cable tho
what do you think the current is of a 10.9kw heater?
Old 22-06-2005, 08:12 PM
  #21  
KSA-Cossie
Professional Waffler
iTrader: (4)
 
KSA-Cossie's Avatar
 
Join Date: May 2004
Location: Shutting down jap crap
Posts: 25,439
Received 19 Likes on 17 Posts
Default

Nearly 44 amps.
Old 22-06-2005, 08:13 PM
  #22  
Graceland
Team HOTHOT!

 
Graceland's Avatar
 
Join Date: Aug 2003
Location: Huddersfield Drives: Trains ;)
Posts: 19,065
Received 1 Like on 1 Post
Default

45.41 amps

i'd install 60 amp cable minimum to take into account the ambient temperature, voltage drop and starting current for the heater in the shower
Old 22-06-2005, 08:16 PM
  #23  
GARETH T
Professional Waffler
 
GARETH T's Avatar
 
Join Date: May 2003
Location: barry-south wales
Posts: 30,980
Received 9 Likes on 6 Posts
Default

i always work it out on 230 volts to be on the safer side
Old 22-06-2005, 08:18 PM
  #24  
Brasso
Advanced PassionFord User
 
Brasso's Avatar
 
Join Date: May 2003
Location: Sunny Burton.
Posts: 1,833
Likes: 0
Received 0 Likes on 0 Posts
Default

47 amps at 230v. You need 10mm twin and earth minimum. You'll never run it at full chat tho. Make sure its wired through a shower isolator/pull cord.

Part P is a pain in the fookin ass. More money scamming.
Old 22-06-2005, 08:19 PM
  #25  
BillyCabrio
10K+ Poster!!
Thread Starter
iTrader: (1)
 
BillyCabrio's Avatar
 
Join Date: Jun 2003
Location: Dartford, Kent - Home of the two way one way system.
Posts: 13,450
Received 2 Likes on 2 Posts
Default

Oh gawd what have i started..................
Old 22-06-2005, 08:48 PM
  #26  
plynchy
PassionFord Post Troll
 
plynchy's Avatar
 
Join Date: Apr 2004
Location: "Sunny" Redcar
Posts: 2,895
Likes: 0
Received 2 Likes on 2 Posts
Default

10 mm twin & earth.
The End.

Old 22-06-2005, 08:55 PM
  #27  
Eagle
Super Moderator


iTrader: (2)
 
Eagle's Avatar
 
Join Date: Jun 2003
Location: somwhere in wow
Posts: 18,586
Received 4 Likes on 4 Posts
Default

Originally Posted by GARETH T
i always work it out on 230 volts to be on the safer side
always a good idea...
Old 23-06-2005, 08:36 AM
  #28  
*Anna*
PassionFord Post Whore!!
 
*Anna*'s Avatar
 
Join Date: Jul 2003
Location: Sauf LDN Mate!!!!
Posts: 5,038
Likes: 0
Received 0 Likes on 0 Posts
Default

WOW all this to wire up a shower.
Old 23-06-2005, 08:58 AM
  #29  
Paul Eggleton
PassionFord Post Whore!!
 
Paul Eggleton's Avatar
 
Join Date: Jun 2003
Location: Saving the planet
Posts: 5,749
Likes: 0
Received 0 Likes on 0 Posts
Default

Originally Posted by *Anna*
WOW all this to wire up a shower.
And I bet it was a women who asked him to do it, thinking its a five minute job

Sometimes you have no idea