I've just bought a 10.9kw Mira shower, whats the thickness cable i need?

Is it ok to put a short piece of wire on it with a plug and plug it into the extension lead?

Reply
Old Jun 22, 2005 | 07:08 PM
  #2  
BillyCabrio's Avatar
BillyCabrio
Thread Starter
10K+ Poster!!
iTrader: (1)
 
Joined: Jun 2003
Posts: 13,450
Likes: 2
From: Dartford, Kent - Home of the two way one way system.
Default

Not really I do know better than that!

Just wanna double check its the same cable as Electric cooker applications?

Along with the double pole switch and RCD in the fuse box

Cheers lol
Reply
Old Jun 22, 2005 | 07:11 PM
  #3  
Graceland's Avatar
Graceland
Team HOTHOT!
 
Joined: Aug 2003
Posts: 19,065
Likes: 1
From: Huddersfield Drives: Trains ;)
Default

4mm twin and earth, on its own circuit breaker in the consumer unit - need to have a 16ms trip time so the breaker is a catagory B one i think - was years ago when i did all this at college
Reply
Old Jun 22, 2005 | 07:21 PM
  #4  
BillyCabrio's Avatar
BillyCabrio
Thread Starter
10K+ Poster!!
iTrader: (1)
 
Joined: Jun 2003
Posts: 13,450
Likes: 2
From: Dartford, Kent - Home of the two way one way system.
Default

Yeah i knew about the breaker, so 4mm then. Cheers.
Reply
Old Jun 22, 2005 | 07:22 PM
  #5  
focusv8's Avatar
focusv8
PassionFord Post Whore!!
20 Year Member
Liked
Loved
 
Joined: Sep 2004
Posts: 4,773
Likes: 86
From: Nottingham
Default

It needs to be AT LEAST 10mm twin and earth, depends how long the cable is going to be. (earth loop impedance) or you better get an insurance claim form ready.

Disclaimer:

Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
Reply
Old Jun 22, 2005 | 07:24 PM
  #6  
Graceland's Avatar
Graceland
Team HOTHOT!
 
Joined: Aug 2003
Posts: 19,065
Likes: 1
From: Huddersfield Drives: Trains ;)
Default

10mm twin and earth - thats way to heavy - we never used to even fit anything above 4mm armoured for 12kw machinery when i was a maintenance bod
Reply
Old Jun 22, 2005 | 07:28 PM
  #7  
GARETH T's Avatar
GARETH T
Professional Waffler
20 Year Member
 
Joined: May 2003
Posts: 30,980
Likes: 9
From: barry-south wales
Default

i havent got my cablee tables at home with me (anyone got the 16th edition iee?) but im sure you on the edge of 10mm, but it should be fine

of cause it all depends on the cable run
Reply
Old Jun 22, 2005 | 07:29 PM
  #8  
GARETH T's Avatar
GARETH T
Professional Waffler
20 Year Member
 
Joined: May 2003
Posts: 30,980
Likes: 9
From: barry-south wales
Default

Originally Posted by Graceland
10mm twin and earth - thats way to heavy - we never used to even fit anything above 4mm armoured for 12kw machinery when i was a maintenance bod
whats that 3phase machinery though?
Reply
Old Jun 22, 2005 | 07:29 PM
  #9  
focusv8's Avatar
focusv8
PassionFord Post Whore!!
20 Year Member
Liked
Loved
 
Joined: Sep 2004
Posts: 4,773
Likes: 86
From: Nottingham
Default

That'll be 12kw 3 Phase....think about it..
Reply
Old Jun 22, 2005 | 07:30 PM
  #10  
Graceland's Avatar
Graceland
Team HOTHOT!
 
Joined: Aug 2003
Posts: 19,065
Likes: 1
From: Huddersfield Drives: Trains ;)
Default

thats a good point - 3 different phases to distrbute the current - my excuse is i aint put any of the theory into practice in about 4 years
Reply
Old Jun 22, 2005 | 07:32 PM
  #11  
Graceland's Avatar
Graceland
Team HOTHOT!
 
Joined: Aug 2003
Posts: 19,065
Likes: 1
From: Huddersfield Drives: Trains ;)
Default

voltage drop, ambient temperature, resistence of the cable and heat generation are more of a factor in single phase from what i remember - its ages since i studdied it, might have to dig my 16th edition regs book out
Reply
Old Jun 22, 2005 | 07:35 PM
  #12  
GARETH T's Avatar
GARETH T
Professional Waffler
20 Year Member
 
Joined: May 2003
Posts: 30,980
Likes: 9
From: barry-south wales
Default

might have to dig my 16th edition regs book out

ya its an exciting coarse isnt it
Reply
Old Jun 22, 2005 | 07:36 PM
  #13  
Graceland's Avatar
Graceland
Team HOTHOT!
 
Joined: Aug 2003
Posts: 19,065
Likes: 1
From: Huddersfield Drives: Trains ;)
Default

never did the 16th edition course - i walked out of my job, they were going to put me thru it tho - kinda wish i stayed now and got 16th edition qualified - altho i left with onc and hnc in electrical engineering - but i've forgotten nearly all of it
Reply
Old Jun 22, 2005 | 07:44 PM
  #14  
Graceland's Avatar
Graceland
Team HOTHOT!
 
Joined: Aug 2003
Posts: 19,065
Likes: 1
From: Huddersfield Drives: Trains ;)
Default

http://www.tlc-direct.co.uk/Book/4.3.9.htm

data and cable tables
Reply
Old Jun 22, 2005 | 07:54 PM
  #15  
BillyCabrio's Avatar
BillyCabrio
Thread Starter
10K+ Poster!!
iTrader: (1)
 
Joined: Jun 2003
Posts: 13,450
Likes: 2
From: Dartford, Kent - Home of the two way one way system.
Default

Originally Posted by focusv8
Disclaimer:

Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
I'm aware of the new regs, all i wanna do is the cable run to save on labour cost. I'll get a sparkie to connect it either end.

I'll ask a sparkie at work tomorrow.
Reply
Old Jun 22, 2005 | 07:58 PM
  #16  
KSA-Cossie's Avatar
KSA-Cossie
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

10 mm twin and earth m8.
Reply
Old Jun 22, 2005 | 08:01 PM
  #17  
GARETH T's Avatar
GARETH T
Professional Waffler
20 Year Member
 
Joined: May 2003
Posts: 30,980
Likes: 9
From: barry-south wales
Default

focusv8,
Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.

the mad thing is,, my boss is charman of the south wales IEE, he bought a house for his girl, the morgage company wanted a certificate to say the electrics of the house was up too spec,,,,, he wasnt alowed to write one as he wasnt approved
Reply
Old Jun 22, 2005 | 08:07 PM
  #18  
Graceland's Avatar
Graceland
Team HOTHOT!
 
Joined: Aug 2003
Posts: 19,065
Likes: 1
From: Huddersfield Drives: Trains ;)
Default

thats a bit shit really
Reply
Old Jun 22, 2005 | 08:08 PM
  #19  
BillyCabrio's Avatar
BillyCabrio
Thread Starter
10K+ Poster!!
iTrader: (1)
 
Joined: Jun 2003
Posts: 13,450
Likes: 2
From: Dartford, Kent - Home of the two way one way system.
Default

I'm 99.9% sure its a 45amp rated cable tho
Reply
Old Jun 22, 2005 | 08:10 PM
  #20  
GARETH T's Avatar
GARETH T
Professional Waffler
20 Year Member
 
Joined: May 2003
Posts: 30,980
Likes: 9
From: barry-south wales
Default

Originally Posted by BillyCabrio
I'm 99.9% sure its a 45amp rated cable tho
what do you think the current is of a 10.9kw heater?
Reply
Old Jun 22, 2005 | 08:12 PM
  #21  
KSA-Cossie's Avatar
KSA-Cossie
Professional Waffler
iTrader: (4)
 
Joined: May 2004
Posts: 25,439
Likes: 19
From: Shutting down jap crap
Default

Nearly 44 amps.
Reply
Old Jun 22, 2005 | 08:13 PM
  #22  
Graceland's Avatar
Graceland
Team HOTHOT!
 
Joined: Aug 2003
Posts: 19,065
Likes: 1
From: Huddersfield Drives: Trains ;)
Default

45.41 amps

i'd install 60 amp cable minimum to take into account the ambient temperature, voltage drop and starting current for the heater in the shower
Reply
Old Jun 22, 2005 | 08:16 PM
  #23  
GARETH T's Avatar
GARETH T
Professional Waffler
20 Year Member
 
Joined: May 2003
Posts: 30,980
Likes: 9
From: barry-south wales
Default

i always work it out on 230 volts to be on the safer side
Reply
Old Jun 22, 2005 | 08:18 PM
  #24  
Brasso's Avatar
Brasso
Advanced PassionFord User
 
Joined: May 2003
Posts: 1,833
Likes: 0
From: Sunny Burton.
Default

47 amps at 230v. You need 10mm twin and earth minimum. You'll never run it at full chat tho. Make sure its wired through a shower isolator/pull cord.

Part P is a pain in the fookin ass. More money scamming.
Reply
Old Jun 22, 2005 | 08:19 PM
  #25  
BillyCabrio's Avatar
BillyCabrio
Thread Starter
10K+ Poster!!
iTrader: (1)
 
Joined: Jun 2003
Posts: 13,450
Likes: 2
From: Dartford, Kent - Home of the two way one way system.
Default

Oh gawd what have i started..................
Reply
Old Jun 22, 2005 | 08:48 PM
  #26  
plynchy's Avatar
plynchy
PassionFord Post Troll
 
Joined: Apr 2004
Posts: 2,895
Likes: 2
From: "Sunny" Redcar
Default

10 mm twin & earth.
The End.

Reply
Old Jun 22, 2005 | 08:55 PM
  #27  
Eagle's Avatar
Eagle
Super Moderator
20 Year Member
iTrader: (2)
 
Joined: Jun 2003
Posts: 18,610
Likes: 4
From: somwhere in wow
Default

Originally Posted by GARETH T
i always work it out on 230 volts to be on the safer side
always a good idea...
Reply
Old Jun 23, 2005 | 08:36 AM
  #28  
*Anna*'s Avatar
*Anna*
PassionFord Post Whore!!
 
Joined: Jul 2003
Posts: 5,038
Likes: 0
From: Sauf LDN Mate!!!!
Default

WOW all this to wire up a shower.
Reply
Old Jun 23, 2005 | 08:58 AM
  #29  
Paul Eggleton's Avatar
Paul Eggleton
PassionFord Post Whore!!
 
Joined: Jun 2003
Posts: 5,749
Likes: 0
From: Saving the planet
Default

Originally Posted by *Anna*
WOW all this to wire up a shower.
And I bet it was a women who asked him to do it, thinking its a five minute job

Sometimes you have no idea