I've just bought a 10.9kw Mira shower, whats the thickness cable i need?
Is it ok to put a short piece of wire on it with a plug and plug it into the extension lead?
Is it ok to put a short piece of wire on it with a plug and plug it into the extension lead?
Thread Starter
10K+ Poster!!
iTrader: (1)
Joined: Jun 2003
Posts: 13,450
Likes: 2
From: Dartford, Kent - Home of the two way one way system.
Not really
I do know better than that!
Just wanna double check its the same cable as Electric cooker applications?
Along with the double pole switch and RCD in the fuse box
Cheers lol
I do know better than that!Just wanna double check its the same cable as Electric cooker applications?
Along with the double pole switch and RCD in the fuse box
Cheers lol
4mm twin and earth, on its own circuit breaker in the consumer unit - need to have a 16ms trip time so the breaker is a catagory B one i think - was years ago when i did all this at college
It needs to be AT LEAST 10mm twin and earth, depends how long the cable is going to be. (earth loop impedance) or you better get an insurance claim form ready.
Disclaimer:
Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
Disclaimer:
Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
i havent got my cablee tables at home with me (anyone got the 16th edition iee?) but im sure you on the edge of 10mm, but it should be fine
of cause it all depends on the cable run
of cause it all depends on the cable run
Trending Topics
Originally Posted by Graceland
10mm twin and earth
- thats way to heavy - we never used to even fit anything above 4mm armoured for 12kw machinery when i was a maintenance bod 
- thats way to heavy - we never used to even fit anything above 4mm armoured for 12kw machinery when i was a maintenance bod 
voltage drop, ambient temperature, resistence of the cable and heat generation are more of a factor in single phase from what i remember - its ages since i studdied it, might have to dig my 16th edition regs book out
never did the 16th edition course - i walked out of my job, they were going to put me thru it tho - kinda wish i stayed now and got 16th edition qualified - altho i left with onc and hnc in electrical engineering - but i've forgotten nearly all of it
Thread Starter
10K+ Poster!!
iTrader: (1)
Joined: Jun 2003
Posts: 13,450
Likes: 2
From: Dartford, Kent - Home of the two way one way system.
Originally Posted by focusv8
Disclaimer:
Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
I'll ask a sparkie at work tomorrow.
focusv8,
the mad thing is,, my boss is charman of the south wales IEE, he bought a house for his girl, the morgage company wanted a certificate to say the electrics of the house was up too spec,,,,, he wasnt alowed to write one as he wasnt approved
Since 1st January 2005 electrical installations in domestic properties come under building regs part P.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
This restricts installation of new wiring to approved contractors, or subject to building regs approval amd inspection, for a fee of course.
the mad thing is,, my boss is charman of the south wales IEE, he bought a house for his girl, the morgage company wanted a certificate to say the electrics of the house was up too spec,,,,, he wasnt alowed to write one as he wasnt approved
47 amps at 230v. You need 10mm twin and earth minimum. You'll never run it at full chat tho. Make sure its wired through a shower isolator/pull cord.
Part P is a pain in the fookin ass. More money scamming.