Recommend me a compressor?
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
Hi all,
I'm after a single phase compressor, budget £600... What's good and what's not?
I'm looking at this Clarke one at the mo, http://www.machinemart.co.uk/shop/pr...air-compressor
Thanks, Yodi
I'm after a single phase compressor, budget £600... What's good and what's not?
I'm looking at this Clarke one at the mo, http://www.machinemart.co.uk/shop/pr...air-compressor
Thanks, Yodi
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
Sorry I put single phase as thats all I thought that counted, no idea but I know my plug sockets are on a 32 amp ring?
How about this one ?
http://www.ebay.co.uk/itm/Compressor...item336e4fd560
How about this one ?
http://www.ebay.co.uk/itm/Compressor...item336e4fd560
If your just on 3pin plug it's 13 amp as for finding anything else owt mate i'm lost as i'm not a sparky lol but on the compressor he put the link up for needs a 16amp minimum feed
Trending Topics
Clark are over rated and can be difficult to obtain parts for,seally are overpriced...ERP are a really good make and based in hull..£600 should get u a decent machine,ones on british built air tanks are better than the italian crap the more you spend the better machine you will get mate..
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
Thanks for the advice, £600 really is the budget I'm looking to spend I'd gladly spend that on a used one to get a better compressor
Clark are over rated and can be difficult to obtain parts for,seally are overpriced...ERP are a really good make and based in hull..£600 should get u a decent machine,ones on british built air tanks are better than the italian crap the more you spend the better machine you will get mate..
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
Ah really, so what sort of current draw does it pull then?
My electricians coming tomorrow to see if its ok to run it and if I have space, I have a 4ton 2 post ramp on the plug cicuit so can't add the compressor to that too.
My electricians coming tomorrow to see if its ok to run it and if I have space, I have a 4ton 2 post ramp on the plug cicuit so can't add the compressor to that too.
16 works but obviously 32 is ideal. They are a good comp
Not true matey,we have stopped fixing them as we kept struggling for spares as they never had them in stock..they arnt a bad machine but aftersales can be lousy
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
30 amp is recommended as it's 3hp, i personally wouldnt run anything less but some have and got away with it some have and havnt. Where you based?
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
http://www.machinemart.co.uk/shop/pr...air-compressor
Only buy 4hp mate id your supply is top notch.a louzy supply will not run a 4hp long and u will run into problems with motors running at high amps witch will eventually burn out..3hp is your best bet,i wont sell a 4hp at work as they can be a ball ache
http://www.machinemart.co.uk/shop/pr...air-compressor
I got one of these and i have it linked to fill a 300 lt tank to
I change oil once a month
I got one of these and i have it linked to fill a 300 lt tank to
I change oil once a month
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
The motors burn out and doesn't work, it pops 32 amp breakers of b,c and d ratings..
I took the cover of the wiring off, its own circuit breaker has been bypassed and you see a huge arc in the motor if you try and turn it on
I took the cover of the wiring off, its own circuit breaker has been bypassed and you see a huge arc in the motor if you try and turn it on
Your best bet is to buy a smaller motor.
The issue isnt so much with the 16/32A fuse rating. It's largely down to the size of the supply into the house, cable diameters and volt drop.
If you try and run a huge load of a small cable, the volt drop will be higher, and this in turn increases current draw. And motors starting up draw a lot of current unless there is an inverter or other similar soft start control.
Even a 3HP motor off a 13A outlet, either plug/spur or direct connection will still blow the fuse on startup quite often unless it has a good power supply ( ie cable size ), and if it does survive, the actual switch or plug will melt over time.
You could have what is called a 32A supply from a 2.5 ring....but what feeds the garage ? What cable diameter etc ? How long ? Plus What supplies the house ? Cable diameter etc.
Having a large diameter at the end of a circuit is pointless if it has a long and tiny cable feeding the start.
For any normal domestic household on single phase, 3HP is the absolute max you should consider, and you need a good sized supply conductor direct from source to the power outlet for the motor.
I didnt say cable direct...as naturally it may involve an additional consumer unit etc. But conductor size needs to remain IMO capable of 63A or more until the final dedicated circuit to the compressor. Which even for 3HP, needs to be at least 4mm^2, or better 6mm^2 and a 16A blue 3 pin plug or direct on/off isolator
Even then, when the motor kicks in, lights in the house can likely flicker, and some fluorescent style lighting can knock off and restart.
Another option which will help, is if you can get a soft start setup for it. This will reduce current draw on startup. Although actual running current can still be high.
Ive googled and there are some available, although Ive never used one myself.
Something like this, no idea on cost though. You'd need to speak to someone with more experience though to check actual suitability
http://www.schneider-electric.co.uk/...istart-01.page
The issue isnt so much with the 16/32A fuse rating. It's largely down to the size of the supply into the house, cable diameters and volt drop.
If you try and run a huge load of a small cable, the volt drop will be higher, and this in turn increases current draw. And motors starting up draw a lot of current unless there is an inverter or other similar soft start control.
Even a 3HP motor off a 13A outlet, either plug/spur or direct connection will still blow the fuse on startup quite often unless it has a good power supply ( ie cable size ), and if it does survive, the actual switch or plug will melt over time.
You could have what is called a 32A supply from a 2.5 ring....but what feeds the garage ? What cable diameter etc ? How long ? Plus What supplies the house ? Cable diameter etc.
Having a large diameter at the end of a circuit is pointless if it has a long and tiny cable feeding the start.
For any normal domestic household on single phase, 3HP is the absolute max you should consider, and you need a good sized supply conductor direct from source to the power outlet for the motor.
I didnt say cable direct...as naturally it may involve an additional consumer unit etc. But conductor size needs to remain IMO capable of 63A or more until the final dedicated circuit to the compressor. Which even for 3HP, needs to be at least 4mm^2, or better 6mm^2 and a 16A blue 3 pin plug or direct on/off isolator
Even then, when the motor kicks in, lights in the house can likely flicker, and some fluorescent style lighting can knock off and restart.
Another option which will help, is if you can get a soft start setup for it. This will reduce current draw on startup. Although actual running current can still be high.
Ive googled and there are some available, although Ive never used one myself.
Something like this, no idea on cost though. You'd need to speak to someone with more experience though to check actual suitability
http://www.schneider-electric.co.uk/...istart-01.page
Last edited by stevieturbo; Nov 17, 2011 at 09:35 PM.
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
Thanks for your help mate, the compressor is in an industrial unit and all the wiring is new and well up to the job.
I just worry about a new motor and it not fitting or being wrong and then have all the added hassle.
I just worry about a new motor and it not fitting or being wrong and then have all the added hassle.
Steve you sound like you know the dance, my garage is fused in the houses fusebox with a 60amp fuse, I know you can't say for definate but do you think I would be ok with a 2.5hp 7.5 amp compressor, its a new item I've found on ebay. I presume this would go on a standard 3 pin plug?
And just because it is in an industrial unit, means nothing.
I worked as a spark for around 15 years, and some of the things you see people using are unbelievable. Whether just shoddy work, or undersized cables, terminations, etc etc
Unless you have a minimum of 6mm^2 from the incoming Electric Board mains to the compressor connection point itself, then IMO it is not sufficient.
At the minute you still dont know why the unit doesnt work. Just that it doesnt work, and internal parts had been tampered with.
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
Stu 7.5 am would be more than ok on a 13amp plug...
Stevie and jenrst, do you really think I should change the motor to a spec down and get a 3hp one?
Stevie and jenrst, do you really think I should change the motor to a spec down and get a 3hp one?
Thread Starter
I've found that life I needed.. It's HERE!!
iTrader: (1)
Joined: May 2003
Posts: 1,334
Likes: 3
From: North London
We posted at the same time, the electrician told me also its the motor they are £160 new is it really worth trying to get that one repaired?
Should I see if I can get a 3hp one instead, any idea what fits? Thanks for your help
Should I see if I can get a 3hp one instead, any idea what fits? Thanks for your help
Steve you sound like you know the dance, my garage is fused in the houses fusebox with a 60amp fuse, I know you can't say for definate but do you think I would be ok with a 2.5hp 7.5 amp compressor, its a new item I've found on ebay. I presume this would go on a standard 3 pin plug?
These are the important parts.
You could put 60A fuse after 60A fuse. But if the original incoming supply is only capable of 60A too....then clearly you're fighting a losing battle.
It would be like having ten fire hoses to extinguish a fire.....except they are all fed by a single fire hose at the origin. So by the time it gets to the outlet, it's just a dribble.
Fuse ratings dont indicate what a power circuit has to offer. They are purely protection for the wiring itself so the fuse should blow before wiring goes on fire.
2.5HP "should" be ok. But again, you cant overlook starting current. That's what will blow the fuse, not the normal 7.5A running current. And again, if the actual power supply is limited by cable size ( again, see volts as water flow in above ) then that current will rise.
But it's an easy fix to install an isolator with either a separate fuse or motor rated breaker. Or you could rely on the fuse at the fuse box.
Again, the fuses are not to protect equipment, they are primarily to protect wiring, or short circuits/fire risk.
Using a 13A plug, this will be the highest risk area for the current passing through. I did run one for a while through a plug top with 6mm bolt as a fuse lol.
The actual pins of the plug welded themselves to the socket such was the arcing due to a poor connection for the current involved.
And with arcing, comes a fire risk.
Last edited by stevieturbo; Nov 17, 2011 at 09:54 PM.
http://www.ebay.co.uk/itm/NEILESEN-5...92461791589456
This is the 1 I might chance
Sounds like I better get the fatherin law and bro in law to check this out for me. (sparkies)
Cheers again steve
This is the 1 I might chance
Sounds like I better get the fatherin law and bro in law to check this out for me. (sparkies)
Cheers again steve
Last edited by studabear; Nov 17, 2011 at 10:01 PM.
At least new, yes you know exactly what you have.
If you think you're electrical supply is up to handling the 4HP motor, then replace like for like.
But as already mentioned, unless you are sure you have a substantial power supply available, I wouldnt do it on single phase.