I need to run some cable underground to my garage, approx 40m run, needs to be able to power 16 amp welder and lathe, milling machine inverter ect, socket on the mig is a blue 16 amp connector, what size of cable would you recommend ?
Regards
Mark
Regards
Mark
Are you coming out of your household consumer unit? Ideally, you need to come off your consumer unit and go direct to a separate consumer unit with RCD for the garage. You want the cable under you garden to be SWA (Armoured cable) but also protected incase of any damage etc, hence coming out of your household consumer unit..... 6mm2 SWA will be ideal and will cost you about £125inc VAT for a 50m roll.
All qualified electricians feel free to add!! I'm still at college learning the trade!!
All qualified electricians feel free to add!! I'm still at college learning the trade!!
Are you coming out of your household consumer unit? Ideally, you need to come off your consumer unit and go direct to a separate consumer unit with RCD for the garage. You want the cable under you garden to be SWA (Armoured cable) but also protected incase of any damage etc, hence coming out of your household consumer unit..... 6mm2 SWA will be ideal and will cost you about £125inc VAT for a 50m roll.
All qualified electricians feel free to add!! I'm still at college learning the trade!!
All qualified electricians feel free to add!! I'm still at college learning the trade!!
i expected about a ton or so to buy.
If your not going to have everything on at the same time, then you could get away with a 4mm SWA but could do with knowing what the total power for the garage is and is there a chance of a few of the said machines been on at the same time???
there will never be more than one machine on at once, im good but not that good, lighting, prob 20 fluorescents, 1hp motors on the machines one at once, never alot being drawn in one go, tig plant, mig plant, i would be surprised if i ever saw any more than 25 amps in one go, lets put it this way, they were all in my old place and I have a 20amp breaker feeding the garage, and only under full chat with the mig and all lights on did it every now and again trip the switch.
Trending Topics
there will never be more than one machine on at once, im good but not that good, lighting, prob 20 fluorescents, 1hp motors on the machines one at once, never alot being drawn in one go, tig plant, mig plant, i would be surprised if i ever saw any more than 25 amps in one go, lets put it this way, they were all in my old place and I have a 20amp breaker feeding the garage, and only under full chat with the mig and all lights on did it every now and again trip the switch.
In that case 6mm SWA will give you around 36A
ask a few questions stir a little interest and gain advice from people doing the job day in day out - especially when you find someone who says 'ive got a spare 50m left over from a job - yours for £50 - then im happy
Sounds like 6mm it will be
I always try to come in under budget Jake 
ask a few questions stir a little interest and gain advice from people doing the job day in day out - especially when you find someone who says 'ive got a spare 50m left over from a job - yours for £50 - then im happy
Sounds like 6mm it will be
cheers guys.
ask a few questions stir a little interest and gain advice from people doing the job day in day out - especially when you find someone who says 'ive got a spare 50m left over from a job - yours for £50 - then im happy
Sounds like 6mm it will be
Now I'm not suggesting I do that at work but its possible some of my central heating pipework was for free.... lol....
The shit we throw away is crackers and as for SWA stuff... you could get rich quick..
lol - too true - i think thats where half the stuff on ebay comes from !
I personally would not come straight off the mains. Although I'm not 100% clued up. Surely, if you come straight off the mains with the SWA then you will not be protecting the cable if for some reason it gets cut through in the garden. I know its armoured but that means nothing to heavy machinery...
I personally would not come straight off the mains. Although I'm not 100% clued up. Surely, if you come straight off the mains with the SWA then you will not be protecting the cable if for some reason it gets cut through in the garden. I know its armoured but that means nothing to heavy machinery...
although, that said, depending on how old the consumer unit is, he may need to have it upgraded as it may not be suitable to have that much load running from it
my electrics knowledge is close to 20 years old and lots have changed in that time, but you always always overspec electrics as it's the one time you want to make sure everything is as safe from overload as possible, don't skimp on £25 if it's the difference between doing a half arsed job or doing a proper job, you dn't want to be running to the tripped rcd every 5 minutes when you've just set up the tig to start welding