upstairs lights went off lastnight, the breaker has tripped in the garage.

but no matter what we try the breaker won't switch back on its getting anoying now with having no light upstairs so having use lamps

thanks for any help

chris
Reply
Old Oct 1, 2006 | 07:27 PM
  #2  
Eagle's Avatar
Eagle
Super Moderator
20 Year Member
iTrader: (2)
 
Joined: Jun 2003
Posts: 18,610
Likes: 4
From: somwhere in wow
Default

as it wont reset i can only guess at the fact there is a short somewhere .. either one of the lamps has given up or the wireing .. remove all the upstairs light bulbs and see if it will reset ..
Reply
Old Oct 1, 2006 | 07:28 PM
  #3  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

Take all the lamps out ( bulbs to you) lol and try to reset the breaker, The lamp that blew may still have a fault on it. If it resets then replace the lamps one by one. If you try one and it trips again you found your faulty one

If you have no lamps in and it still won't reset then it's probably a faulty breaker. Write the name of it and the size of it (probably 6 amp) and go to a wholesaler. They are about Ł6. If it's not a faulty breaker then your wiring is faulty and will need a sparky to test it. Hope this helps
Reply
Old Oct 1, 2006 | 07:32 PM
  #4  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

cheers guys will try it now
Reply
Old Oct 1, 2006 | 07:33 PM
  #5  
focusv8's Avatar
focusv8
PassionFord Post Whore!!
20 Year Member
Liked
Loved
 
Joined: Sep 2004
Posts: 4,773
Likes: 86
From: Nottingham
Default

Have you got a shaver socket in the bathroom, that may be on the same circuit?

Have any light fittings, (bathroom?) been replaced recently?

Any dimmer switches fitted upstairs?

.
Reply
Old Oct 1, 2006 | 07:34 PM
  #6  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

If you have any low voltage lights upstairs then it could be a faulty transformer. Don't remove the lamps just make sure the switch is in the off position. The bottom of the switch should be sticking out if it's off (providing the switch is'nt upside down) If the breaker then resets and it trips when you put the low voltage lights on then it's either a faulty transformer or a dodgy lampholder, these break after a while cos they get fookin hot !!!

It could also be damp / condensation in your bathroom fitting
Reply
Old Oct 1, 2006 | 07:37 PM
  #7  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

all bulbs out still wont reset, will try and get a new breaker asap see if that works
Reply

Trending Topics

Old Oct 1, 2006 | 07:37 PM
  #8  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

when you reset the MCB can you feel it blowing back out or does it just feel loose?

if the mcbs OK it should feel possible hear it blowing out.

next turn off all the switches off on the upstairs circuit, this will illuminate part of the circuit. try resetting the MCB.

If it stays in turn the light on then see which one causes it to trip.

if it still goes off you could start finding the fault if you are OK with electrics, not that you should of course.

You could do this by opening a ceiling rose, and taking all the red/browns out of the centre conector so they aint touching, try turning it on, keep doing this until it resets, then turn off and connect another in, hard to explain really.
Reply
Old Oct 1, 2006 | 07:38 PM
  #9  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

focusv8


yea dimmer switch in my room
Reply
Old Oct 1, 2006 | 07:39 PM
  #10  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

if your certain it may be the mcb, take the cable out of the mcb and try resetting it, if it does trip its defo the mcb, for a tempoary messure you could put the cable into another MCB of the same current ratting.
Reply
Old Oct 1, 2006 | 07:40 PM
  #11  
Eagle's Avatar
Eagle
Super Moderator
20 Year Member
iTrader: (2)
 
Joined: Jun 2003
Posts: 18,610
Likes: 4
From: somwhere in wow
Default

might be the dimmer then ..
Reply
Old Oct 1, 2006 | 07:40 PM
  #12  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

the upstars lights breaker just feels loose just prings back down if you try and swithch it on
Reply
Old Oct 1, 2006 | 07:41 PM
  #13  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

Originally Posted by c.h.r.i.s
focusv8


yea dimmer switch in my room
theres a small chance the dimmer has gone, take the red/brown cable out and try turning on.
Reply
Old Oct 1, 2006 | 07:41 PM
  #14  
Eagle's Avatar
Eagle
Super Moderator
20 Year Member
iTrader: (2)
 
Joined: Jun 2003
Posts: 18,610
Likes: 4
From: somwhere in wow
Default

please do not play with electricity if you are in anyway in doubt of your abilitys ! ! ! ! !
Reply
Old Oct 1, 2006 | 07:42 PM
  #15  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

Make sure you switch the whole consumer unit OFF when you change/replace the breaker cos depending on what board you have, the screw that holds the breaker in will be live even if the breaker being changed is OFF !
Reply
Old Oct 1, 2006 | 07:44 PM
  #16  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

take the cable out mate and just try resseting it to see if it holds in, how old is the fuse board, turn the main switch off of course whilst doing it.
Reply
Old Oct 1, 2006 | 07:48 PM
  #17  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

Originally Posted by c.h.r.i.s
the upstars lights breaker just feels loose just prings back down if you try and swithch it on
This is because it still has a fault on the circuit. If it's just the upstairs that has gone, then you will have another 6amp breaker in your board for the downstairs. Connect your wire from your faulty circuit into this and see if it still trips. If it does'nt then your breaker is faulty. If it does then some thing is causing it to trip.
Reply
Old Oct 1, 2006 | 07:49 PM
  #18  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

Originally Posted by Eagle
please do not play with electricity if you are in anyway in doubt of your abilitys ! ! ! ! !
my dad


changing my dimmer to a normal switch now
Reply
Old Oct 1, 2006 | 07:50 PM
  #19  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

live wire into dimmer switch is broke could that be it??
Reply
Old Oct 1, 2006 | 07:51 PM
  #20  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

lol, no need to change it just yet just take the red out to check the problem. Yours adsd nice mine would be telling me to touch it.
Reply
Old Oct 1, 2006 | 07:52 PM
  #21  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

yeah could have been earthing on the metal box, just remake the cable off.
Reply
Old Oct 1, 2006 | 07:52 PM
  #22  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

You could do this by opening a ceiling rose, and taking all the red/browns out of the centre conector so they aint touching, try turning it on, keep doing this until it resets, then turn off and connect another in, hard to explain really.
_________________
If it's wired loop in at the lights he could get in a right pickle doing that lol
Reply
Old Oct 1, 2006 | 07:54 PM
  #23  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

Originally Posted by Series1Dry
You could do this by opening a ceiling rose, and taking all the red/browns out of the centre conector so they aint touching, try turning it on, keep doing this until it resets, then turn off and connect another in, hard to explain really.
_________________
If it's wired loop in at the lights he could get in a right pickle doing that lol
not if he only takes the reds out in the centre block like i said, as they are all permanent lives
Reply
Old Oct 1, 2006 | 07:54 PM
  #24  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

not dimmer, as its still not switching on
Reply
Old Oct 1, 2006 | 07:55 PM
  #25  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

The dimmer could now be fooked mate,take it off and keep the ends of the wires away from each other and then see if your breaker resets
Reply
Old Oct 1, 2006 | 07:57 PM
  #26  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

dimmer has been changed
Reply
Old Oct 1, 2006 | 07:59 PM
  #27  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

And. . . . . ?
Reply
Old Oct 1, 2006 | 07:59 PM
  #28  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

you taken the cable out the mcb just to prove it WILL reset if theres no circuit on it? do that first.
Reply
Old Oct 1, 2006 | 08:02 PM
  #29  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

Originally Posted by Series1Dry
And. . . . . ?
im not an electrician so explain more please

steve on the breaker board?

sorry if i dont understand ant terms/phrases as i not an electrician
Reply
Old Oct 1, 2006 | 08:05 PM
  #30  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

ok, turn off the main switch, everthing should go off, take the cover off, find the mcb and take the small cable out, probably on the top, maby the bottom, put away safely.

put cover back on and turn back on, try to reset. If it resets you defo have a faulty circuit.
Reply
Old Oct 1, 2006 | 08:05 PM
  #31  
danneth's Avatar
danneth
TORQUE!
 
Joined: Sep 2006
Posts: 11,756
Likes: 3
From: Sheffield
Default

tbh just get a sparky in lol

faling that just double it in with something in the board
Reply
Old Oct 1, 2006 | 08:06 PM
  #32  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

Originally Posted by rssteve
Originally Posted by Series1Dry
You could do this by opening a ceiling rose, and taking all the red/browns out of the centre conector so they aint touching, try turning it on, keep doing this until it resets, then turn off and connect another in, hard to explain really.
_________________
If it's wired loop in at the lights he could get in a right pickle doing that lol
not if he only takes the reds out in the centre block like i said, as they are all permanent lives
Yeah but say he did that on all of them and the breaker reset. Then he started to replace them at the end of the circuit and finishing at the first rose that the main first comes into. Then he connected the first rose back up on the circuit. He would'nt know between which 2 lights the fault was would he ! lol
Reply
Old Oct 1, 2006 | 08:09 PM
  #33  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

don't connect them all, just one at a time until it lights up, then work on.
Reply
Old Oct 1, 2006 | 08:12 PM
  #34  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

right dads decided to get someone in, he said he dont feel safe doing anymore thatn he's done

so thanks for your help guys it was worh a try, but like i said he wasnt comfortable going anyfurther.

thanks again for your time

chris
Reply
Old Oct 1, 2006 | 08:13 PM
  #35  
rssteve's Avatar
rssteve
Advanced PassionFord User
 
Joined: Mar 2006
Posts: 1,686
Likes: 0
Default

let us no what the outcome was tho.
Reply
Old Oct 1, 2006 | 08:14 PM
  #36  
c.h.r.i.s's Avatar
c.h.r.i.s
Thread Starter
PassionFord Post Troll
 
Joined: Apr 2006
Posts: 2,773
Likes: 0
From: Wigan
Default

yea will do
Reply
Old Oct 2, 2006 | 07:19 AM
  #37  
Eagle's Avatar
Eagle
Super Moderator
20 Year Member
iTrader: (2)
 
Joined: Jun 2003
Posts: 18,610
Likes: 4
From: somwhere in wow
Default

Originally Posted by danneth
tbh just get a sparky in lol

faling that just double it in with something in the board
sorry but that is just plain silly and dangerous...
Reply
Old Oct 2, 2006 | 04:47 PM
  #38  
Series1Dry's Avatar
Series1Dry
Too many posts.. I need a life!!
 
Joined: Jun 2006
Posts: 882
Likes: 0
From: Cumbriashire
Default

Originally Posted by Eagle
Originally Posted by danneth
tbh just get a sparky in lol

faling that just double it in with something in the board
sorry but that is just plain silly and dangerous...
Not if he puts it in the same size breaker it is'nt.
Reply
Old Oct 2, 2006 | 04:58 PM
  #39  
Anonymous's Avatar
Anonymous
Banned
 
Joined: Dec 2002
Posts: 142
Likes: 1
Default

Originally Posted by c.h.r.i.s
right dads decided to get someone in, he said he dont feel safe doing anymore thatn he's done

so thanks for your help guys it was worh a try, but like i said he wasnt comfortable going anyfurther.

thanks again for your time

chris


best way to go m8

hope it dont cost the earth tho
Reply
Old Oct 2, 2006 | 05:57 PM
  #40  
Eagle's Avatar
Eagle
Super Moderator
20 Year Member
iTrader: (2)
 
Joined: Jun 2003
Posts: 18,610
Likes: 4
From: somwhere in wow
Default

Originally Posted by Series1Dry
Originally Posted by Eagle
Originally Posted by danneth
tbh just get a sparky in lol

faling that just double it in with something in the board
sorry but that is just plain silly and dangerous...
Not if he puts it in the same size breaker it is'nt.
so doubling up on another breaker the same size is ok with you then ...

as it aint with me ... oh well glad i will never have you do any wireing for me then ...