Originally Posted by
KSA-Cossie
The 0.58 depends on how your s/d starter is laid out though m8.
you are right of cause, if the thermal overload is on the delta contactor it should be set to 0.58 FLC,
i dont really like doing this method, as generally everyone over rates there motor size when designing a system and the motor never runs anywhere near FLC, so i always test!