Several things;
Don't pull an earth spike out or disconnect the earth while the supply is switched on, you remove the protection for the installation and risk persons being harmed. (but you know that).
Don't pull an earth spike out and move it UNLESS you have the equipment to test it BEFORE it's connected up and the supply re-instated.
Is the split load board part RCD or twin RCD?
If part then the unprotected part could have high live to earth leakage.
If twin you could still have 58milliamp to earth and not trip either RCD.
Even if the whole installation is 30ma RCD protected, you can still get a shock, whether between the wiring earth and spike (as you did) as it's after the RCD, or between wiring and a person within the protection of the RCD.
29milliamp HURTS won't trip the RCD, but shouldn't kill you.
It's unusual nowadays to have no leakage to earth.
.
Cheers, the RCD only does the sockets and if I switch off all the MCB's to the sockets the voltage leak goes away. I've just been too lazy to go around the whole house and unplug everything to check

, been told it could be power supply transfomers in all the houshold gadgets that can do it ???