My boiler flue (combi) currently goes horizontally out of my kitchen at a height of 2.2m, is it possible to extend the outlet pipework vertically, to say, go through a conservatory roof??
If not, my plans are fucked.
Ta.
My boiler flue (combi) currently goes horizontally out of my kitchen at a height of 2.2m, is it possible to extend the outlet pipework vertically, to say, go through a conservatory roof??
If not, my plans are fucked.
Ta.
#4
10K+ Poster!!
Do you still have installation instructions?
usually a dedicated FLUE section in those, detailing exactly what can and cant be done with each boiler.
there are max lengths etc etc
usually a dedicated FLUE section in those, detailing exactly what can and cant be done with each boiler.
there are max lengths etc etc
#5
PassionFord Post Troll
Thread Starter
Just been looking, but I presume the vertical flue kits are designed to go straight out of the boiler top, not through 2 90 degree bends.
#6
Too many posts.. I need a life!!
The manufacturers instructions will tell you exactly what you can and can't do with a particular boiler.
Normally there is a maximum length you can go vertically, you can put bends on but for each one you fit you normally lose 0.5 m of overal length.
Normally there is a maximum length you can go vertically, you can put bends on but for each one you fit you normally lose 0.5 m of overal length.
#7
PassionFord Post Whore!!
Baxi install manual for 105HE (can't find E) says vertical flue not allowed after the 90 degree bend on top of the boiler.
So you could rise higher at the boiler and then 90 horizontal, but you can't do another 90 vertical after that, max total is 3mtrs, where a 90 degree bend equals 1 mtr.
Probably the same for the 105E.
.
So you could rise higher at the boiler and then 90 horizontal, but you can't do another 90 vertical after that, max total is 3mtrs, where a 90 degree bend equals 1 mtr.
Probably the same for the 105E.
.
Trending Topics
#11
PassionFord Post Troll
Thread Starter
Originally Posted by rapidcossie
can you not get the boiler moved?
Actually the 105HE is a condensor, mine isn't. Wonder if that makes a difference?
Will have a word with the supplier tomorrow...
#12
Too many posts.. I need a life!!
Scroll down to page 16 and it will tell you exactly what you can and can't do
Max vertical flue length 4m, each 45 bend=0.5m each 90 bend=1m
http://www.baxi.co.uk/products/liter...Baxi_Combi.pdf
Cheers.
Max vertical flue length 4m, each 45 bend=0.5m each 90 bend=1m